60Hz US Power Grid and precision timekeeping


I think I'm missing the point of the strategies in regulating the 60 Hz frequency of the US power grid.

I have not found one single reference that explains everything in a way that seems reasonable.

But I have pieced together an unreasonable story using many references.

Apparently, the US power grid is in about 4 segments that do not maintain phase relationships between them. I'm in the largest one, which handles the Eastern US. For mine (or for any of the others by itself), the power company recognizes that it is hard to bring generators online if you don't know the phase you have to match.

Back in the day, people would add a generator to a polyphase AC system by stringing lightbulbs in a circle and adjusting the generator speed to make the light stop chasing around the circle, and then throw the switch. Now it's more complicated of course.

So what they do is keep the phase under very precise control, by guaranteeing that there will be 5,184,000 cycles in any day (that's 60 times the number of seconds in a day, 86400).

But they let this thing get several cycles out of phase during the day, and trim things at the end of the day to hit the 5184000 mark precisely at midnight.

Note that if they do it this way, it actually doesn't make bringing a generator on line any easier. As long as you're a big part of a cycle out of phase, the timing is worthless.

Note also that when you are bringing a generator on line to match a power grid, you obviously have access to both the generator phase and the power grid phase, so it's not as if you need an accurate clock to do it.

I read that power companies consider the 60 Hz frequency a timing service for which they don't charge.

I also read that on the time scale of a few milliseconds to a few seconds, the physical rotating inertia of all the generating equipment actually forms the reservoir that does load leveling, so it has to be able to speed up or slow down with some freedom. It's obvious they don't regulate steam turbine valves or hydroelectric gates or house-sized deisel generators on a 1 second timescale.

So - anybody an expert on this? Or can you send me someplace that is?

While we're on the subject, everybody should go check out leapsecond.com. It's incredible.
  #2  
Old 12-06-2007, 12:26 PM
PuddingCat is offline
Guest
 
Join Date: May 2006
Location: Great Britain
Posts: 275
Wow. Thanks for this. It's really interesting. Sorry I can't add anything useful but your piqued my interest and I'm going off to research (well, later tonight when the work disasters are over)

tim
  #3  
Old 12-06-2007, 12:51 PM
Kevbo is offline
Guest
 
Join Date: May 2005
Posts: 5,917
It seems to me you are a bit confused about the definitions of frequency, phase, and cycles. I'll attempt an analogy:

Imagine a circular track with race cars on it.

If all the race cars are going the same speed, they all have the same frequency....you could measure this in laps/hour.

If you designate one car as the leader, then you can measure the "phase" of all the other cars by how many degrees they are ahead of, or behind the leader. If the cars are NOT spread all around the track, but pretty much in one bunch, you could use the average positon of that group as a reference instead....and that is what is done on a power grid...the phase of the grid is the average phase of all the alternators attached to it. A few alternators might be at exactly this phase, but most will be either ahead or behind.

In order to change phase, a car has to speed up or slow down for a bit with respect to the leader, then resume driving the same speed as the leader. If it does not resume the same speed, then the phase will keep changing. This means that for part of a lap, or maybe several laps (cycles) one car can have a slightly different speed (frequency) than the leader.

You can keep track of the cycles by counting the total number of laps completed.

OK, enough analogy, lets talk about how it actually works in practice:

One thing you got completely wrong: The phase is NOT kept under any sort of control, precise or otherwise. Attempts ARE made to keep the instantanious frequency around 60 Hz. In order to do this the phase goes all over the place.

Serious effort is put into making the daily average frequency EXACTLY 60 Hz. It seems like you have a good handle on how this is done, but note that it requires tweaking the frequency above or below exactly 60 Hz to accomplish this. This is because the generating stations only have about 50% control over the frequency of the grid. The other part of the control is from the loads, which the utility does not control, and which vary constantly.

When an AC alternator is connected to a large grid, It always runs at synchronous speed determined by the frequency of the grid..

It's intrinsic phase will lead the phase of the grid by an angle known as the power angle. If more torque is applied to the input shaft, the power angle will increase. This will of course require that the speed momentarly increase above syncronous speed. Depending on the size of the grid, and the alternator, this will VERY slightly increase the frequency of the entire grid.

When the grid frequency increases, all the motors connected to the grid speed up a little. This means they put out more power, which utilizes the extra power put in at the alternator.

Adding a motor to the grid lowers the frequency a hair, slowing down all the other motors, Thus the new motor steals power from those already connected...the generators don't have to respond instantly. The decrease in frequency is noted at a control center, and additional capacity is brought on line to compensate.
  #4  
Old 12-06-2007, 04:01 PM
BubbaDog's Avatar
BubbaDog is offline
Charter Member
 
Join Date: Mar 2003
Location: KC MO or there abouts
Posts: 5,751
Quote:
Originally Posted by Napier
I think I'm missing the point of the strategies in regulating the 60 Hz frequency of the US power grid.

I have not found one single reference that explains everything in a way that seems reasonable.

But I have pieced together an unreasonable story using many references.

Apparently, the US power grid is in about 4 segments that do not maintain phase relationships between them. I'm in the largest one, which handles the Eastern US. For mine (or for any of the others by itself), the power company recognizes that it is hard to bring generators online if you don't know the phase you have to match.
The Separate grids were caused by the fact that the industry started out as small islands of generators and local loads. As the smaller systems grew there were advantages to interconnecting, however the larger the islands grew the more difficult it was to link them up. The US power grids are the result of physical, political, and financial barriers. The East coast and West coast development is bounded by the Rocky mountains. The Texas grid separation is a result of Texas financial and political pressure to keep Texas energy governance out of the hands of the feds (no power lines across state borders, no fed interference). At stake was not just the Texas electric business but also the Oil which could be used to produce electricity and export power out of the State. I don't know the reason behind the cause of the NorthEastern grid.

Matching the grid frequency (phase?) to bring a generator on line is essential but not all that difficult with today's technology. The frequency floats ever so slightly due to load but is usually within .02Hz

Quote:
Back in the day, people would add a generator to a polyphase AC system by stringing lightbulbs in a circle and adjusting the generator speed to make the light stop chasing around the circle, and then throw the switch. Now it's more complicated of course.
actually the technology today makes it much easier. Feedback systems to control generator speed can precisely match the grid frequency and its pretty much automatic.

Quote:
So what they do is keep the phase under very precise control, by guaranteeing that there will be 5,184,000 cycles in any day (that's 60 times the number of seconds in a day, 86400).

But they let this thing get several cycles out of phase during the day, and trim things at the end of the day to hit the 5184000 mark precisely at midnight.
Time correction isn't necessarily daily. Sometimes the correction period isn't scheduled until a error threshold is reached. Usually the largest utility in the region is responsible for coordinating the process.

Quote:
Note that if they do it this way, it actually doesn't make bringing a generator on line any easier. As long as you're a big part of a cycle out of phase, the timing is worthless.
I think you misunderstand something but I don't follow your statement here. Most time correction is done during off peak times and only lasts a few minutes. During time correction ALL of the generators will slow down (or speed up) to adjust a few 100ths of a cycle to each second. The whole process could occur over a few minutes. If you were bringing a genrator on line during this time it would simply match the frequency of say 59.95hz instead of 60hz. At the end of time correction it would adjust its speed with all of the other genrators on line.

Quote:
Note also that when you are bringing a generator on line to match a power grid, you obviously have access to both the generator phase and the power grid phase, so it's not as if you need an accurate clock to do it.
yep

Quote:
I read that power companies consider the 60 Hz frequency a timing service for which they don't charge.
nice little market spin

Quote:
I also read that on the time scale of a few milliseconds to a few seconds, the physical rotating inertia of all the generating equipment actually forms the reservoir that does load leveling, so it has to be able to speed up or slow down with some freedom. It's obvious they don't regulate steam turbine valves or hydroelectric gates or house-sized deisel generators on a 1 second timescale.
one second-no instantaneously - yes
Automatic controls will operate in order for the unit to maintain speed. The feedback mechanism for all practical purposes is instantaneous. But I see what you mean; the inertia of the rotating mass smooths out the drag on the machine but the power applied to the rotor increases or decreases instantaneously based on the turbines speed.
So - anybody an expert on this? [/quote] IANAExpert - just a DUG
  #5  
Old 12-06-2007, 07:41 PM
Hari Seldon is online now
Member
 
Join Date: Mar 2002
Location: Trantor
Posts: 13,242
This whole thread is interesting. Let me note that Quebec, like Texas is not connected to any other grid. They sell power to New England and New York, so they must have ways of synching.

Back around 1955, I was working in a lab at Penn and we actually tested the frequency occasionally. The test consisted of five tuning rods labeled from 58 to 62 and you judged frequency to about a half CPS by which ones were vibrating the most. We regularly found frequencies anywhere from 59 to 61. We were told that someone in the head offfice of the Philadelphia Electric Company simply adjusted the frequency during the night so that the clock on the wall matched WWV. I don't think they were attached to a grid in those days. Mostly they used coal generating plants, although they owned a dam at Conowingo, just over the Mason-Dixon line in Maryland and perhaps others. But I drove over that dam frequently and it looked like small potatoes.
  #6  
Old 12-06-2007, 09:01 PM
Napier is offline
Charter Member
 
Join Date: Jan 2001
Location: Mid Atlantic, USA
Posts: 9,623
About modern systems being more complicated than light bulbs, and catching up at the end of the day:
http://www.piclist.com/techref/postb...28\100326a.txt
"All generating equipment on a grid has to be running in sync of course, but only the smallest generators can run by just monitoring their own phase lead- that only works if the generator is small enough so that its unable to affect the phase.
"Any large generation facility has to have a reference oscillator and will actively control frequency and power output to achive the desired line voltage and frequency. A Gigiwatt is enough power output to cause large voltage and or frequency fluctuations. Even a Megawatt plant needs to regulate carefully to be sure its help rahter than hurting power quality.
"The power plants use a hierarchy of phase-locked reference oscillators. Nowadays they may be switching to GPS based references, but I suspect that since the system they have is working, it has not been changed.
"There are a few (I think its three in the US) main grid blocks, and each of them has a reference, usually at one of the main generating facilities. (I think one is at Niagra/Horseshoe Falls for the Northeast US and SE Canada, not sure.) This reference is fed (used to be by leased telephone lines, nowadays who knows?) to sub-masters in each area (approximately state by state, but that depends on generator locations, not state lines). Sub-masters feed smaller local power stations.
"Again, these are all phase locked, and they do something to compensate for propagation delays when they set a power plant's reference up.
"So they have a reference. But the original question was, what do they do with it- how good is the frequency regulation? The engineer I talked to (and this was a while ago) said that frequency does vary with load. The grid managers do try to run fast (and therefore high line voltage, by the way) when they are lightly loaded at night to "catch up" to 5184000 cycles per day, they do try to regulate day by day when possible. Unless they go offline (blackout) when all bets are off.

Another reference to cycles per day matching at midnight (though worded vaguely enough that I don't know midnight is to be taken literally) from
http://www.eng-tips.com/viewthread.cfm?qid=171826
"An excess of generation over load will cause the frequency to raise, a deficit of generation will cause the frequency to fall. The power system is operated to provide exactly 5,184,000 cycles per day, midnight-to-midnight and the power output is adjusted as necessary to cause the frequency and cycle count to drift back to where it should be."

A reference with numbers who doesn't think cycles per day is controlled
http://www.sharkyforums.com/archive/.../t-227112.html
"The frequency variation in the American power grid on any given day is between 59.971 and 60.035 HZ.
"Frequency varies with grid load because a higher load will load the generator and slow it down ever so slightly.
"I really don't think that a set number of cycles is maintained each day."

Unattributed article quote:
"The entire North American grid operates at a nominal 60 Hz on four big circuits (one per interconnection) linked by high-voltage dc tie lines. As part of this grid, PJM also must maintain 60 Hz. If a load suddenly draws more current, then a drop in voltage and frequency will occur across the grid, affecting the speed (frequency) of the generators supplying current to the load."

Unattributed article quote:
"The line frequency does vary slightly over the course of the day. (usually decreasing during times of heavy load). At the end of the day, they run slightly faster or slower as needed so that the total line cycles for the day is EXACTLY 5184000. That is, they correct so that the number of line cycles is correct in each midnight-to-midnight period.
"Why is this done? I mean why does the power line need to be EXACTLY 60Hz? Most generators are synchronous machines, when they are connected to the grid, you put torque in and they put power into the line. If you load them down, they are motors and draw power from the line. When you start them up, if the rotation speed and phase is not exactly in synch with the grid, they draw huge fault currents until they synchronize or blow the overload breakers open. So they HAVE to be able to synchronize."


OK, then. This last quote really catches it. BubbaDog, when you say you think I misunderstand something, I agree, and it's right here. They are making the point that hitting the right cumulative cycle count every midnight is somehow helpful whenever they need to bring a generator online, and that this is more or less at the heart of the frequency regulation strategy. I don't think that makes any sense. Sure, you need to adjust the phase relationship between generator and grid so they match before you connect them, but this is only meaningful right around the time you do it. What happened last midnight or will happen next midnight is irrelevant. And yet they appear to be going to a great deal of trouble to achieve this capability, with atomic clocks and leased phone lines and what all.

This "exact count at midnight" thing seems to turn up in many places. Maybe it's some electrical engineering meme that got spread through misunderstanding. It could be that big grids and generators with large moment of inertia have grown more difficult to work with. I know some of the big regional blackouts over recent decades have been blamed on subtle system dynamics. That's what I was thinking when I described modern systems as being more complicated. I think the first quote above hints at this.
  #7  
Old 12-06-2007, 09:32 PM
Napier is offline
Charter Member
 
Join Date: Jan 2001
Location: Mid Atlantic, USA
Posts: 9,623
It keeps coming and coming:

A very pleasant if elementary discussion of time from NIST mentions the grid at
http://tf.nist.gov/general/pdf/461.pdf
"The electric power line is a very good frequency source for many applications. A clock driven from the power line will keep excellent time. This is because the power system is carefully controlled to maintain its frequency within definite limits. Each power company is notified in advance to set its frequency to a particular value, so that the millions of clocks on the system (in homes and offices across the country) will gain or lose time as required to keep the clocks correct. The time corrections are usually done at night."

Fascinating presentation about NIST involvement with phasor stabilization of the grid for reliability improvement
http://www.oe.energy.gov/Documentsan...Stenbakken.pdf
Calibrations Show that System Meets our Goals
Less than 0.01 % magnitude error
Less than 0.2 s time error
< 4.4 mdeg phase error at 60 Hz

Authoritative article from NIST mentions among other things a 10 ms requirement for generator phase control in the grid (in their Table 3)
http://tf.nist.gov/timefreq/general/pdf/2125.pdf
"The electric power system in North America consists of many subsystems that interconnect into several massive grids that span the continent. The system delivers the 60 Hz AC frequency to many millions of customers by matching power generation levels to transmission capability and load patterns. The entire power system relies on time synchronization, and synchronization problems can lead to catastrophic failures. For example, the massive August 2003 blackout in the eastern regions of the United States and Canada was at least partially caused by synchronization failures.
"The timing requirements of the power industry vary (Table 3), because different parts of the system were designed at different times, and the entire system has evolved over many years. The older parts of the system have less stringent timing requirements because they were designed using technologies that predated the Global Positioning System (GPS). The newer parts of the system rely on the ability of GPS to provide precise time synchronization over a large geographic area.
"Since electrical energy must be used as it is generated, generation must be constantly balanced with load, and the alternating current produced by a generator must be kept in approximate phase with every other generator. Generation control requires time synchronization of about 10 ms. Synchronization to about 1 ms is required by event and fault recorders that supply information used to correct problems in the grid and improve operation. Stability control schemes prevent unnecessary generator shutdown, loss of load, and separation of the power grid. They require synchronization to about 46 s (1 phase angle at 60 Hz), and networked controls have requirements one order of magnitude lower, or to 4.6 s (0.1 phase angle at 60 Hz). Traveling wave fault locators find faults in the power grid by timing waveforms that travel down power lines at velocities near the speed of light. Because the high voltage towers are spaced about 300 meters apart, the timing requirement is 1 s, or the period of a 300 meter wavelength. Newer measurement techniques, such as synchronized phasor measurements, require time synchronization to Coordinated Universal Time (UTC) to within 1 s, which corresponds to a phase angle accuracy of 0.022 for a 60 Hz system. A local time reference must be applied to each phasor measurement unit, and GPS is currently the only system that can meet the requirements of synchrophasor measurements. Commercial phasor measurement units that receive GPS signals are shown in Fig. 4.
"The 60 Hz frequency delivered to consumers is sometimes used as the resonator for low priced electric clocks and timers that lack quartz oscillators. The legally allowable tolerance for the 60 Hz frequency is only 0.02 Hz, or 0.033 %, but under normal operating conditions the actual tolerance is much tighter."

Also, BubbaDog, I keep rereading the quote ending in "So they HAVE to be able to synchronize". Maybe I misread it. Maybe he stresses the 60 Hz is for synchronizing generators, not the counts-at-midnight thing. But still it keeps appearing out there - why?
  #8  
Old 12-06-2007, 09:40 PM
Napier is offline
Charter Member
 
Join Date: Jan 2001
Location: Mid Atlantic, USA
Posts: 9,623
And another thing. This gets at the whole system dynamics thing.

When you run a synchronous motor or generator on a system, it can oscillate ahead and behind the phase of the system. You might then worry about whether those oscillations tend to damp out, or tend to grow to the point of jumping a cycle and perhaps catastrophic failure. If I remember right from some work I did a few years ago with synchronous motors, this is a real problem, because most of the things you do to make motors nice and efficient also raise the Q of this harmonic system and leave them vulnerable to oscillations growing uncontrollably. The same thing happens in stepper motors, which are synchronous motors having PM cores and two phase (90 ) windings, and which are often run in open loops without feedback. They actually make viscous oil dampers for stepper motors, cans that mount on the shaft and float an annulus inside a container of viscous oil. They budge the motor off of high Q and towards a rapidly exponentially decaying oscillation, shifting it to the left in the laPlace s-plane. But in big synchronous motors this is very unweildy and messy. They manage it, I think, with things like killer windings that short out the leading and trailing edges of the salient poles so that variation of the magnetic field strength there generates heat, making the oscillations die down.
  #9  
Old 12-06-2007, 09:48 PM
1010011010 is offline
Guest
 
Join Date: Jun 1999
Posts: 2,076
Sounds like the 5184000 cycles per day is a generation/billing issue that has little relevance to the end user.

60Hz was probably chosen intitially for convenience in the control devices available at the time (high precision gearing made for clocks and timers have an affinity for 60) and it's high divisibility means multiphase current peaks are likely to have an integer degree of separation... making generator design and testing a little easier.

Once you've got a lot of electrical equipment out there expecting a given frequency on the line, you're pretty much stuck with it.

If you have multiple independently regulated generators online, it's important to maintain constant frequency or else it's very difficult to control loading of any individual machine. Raising controlled frequency of an AC machine increases carried load (NOT frequency)... decreasing controlled frequency unloads the machine (frequency, again, does not change significantly). Unexpected/uncontrolled changes in machine loading can be unpleasant.
  #10  
Old 12-07-2007, 12:56 AM
mks57 is offline
Guest
 
Join Date: Dec 2003
Location: Seabrook, Maryland
Posts: 3,045
Quote:
Originally Posted by 1010011010
Sounds like the 5184000 cycles per day is a generation/billing issue that has little relevance to the end user.
I used to have a digital clock, built from a kit at a time when digital clocks were unusual. It used a secondary tap from the power transformer to produce a 60 Hz square wave. This signal drove the counter/divider logic in the clock. It was interesting to compare it to WWV. It was never off by more than a second or two. While its short-term accuracy was mediocre, its long-term accuracy was excellent, thanks to the people who run the grid.

Many electro-mechanical clocks used AC synchronous motors, which made their accuracy dependent on the power grid's frequency regulation. Many older computers also used the line frequency to generate their real-time clock. Each cycle on the power line would generate a clock interrupt. The computer's operating system would count the clock interrupts and use them to update the system's time and date.
  #11  
Old 05-24-2012, 12:07 PM
kckay is offline
Guest
 
Join Date: May 2012
Posts: 1

60hz clock


Have heard rumors for years that the Xcel Energy Shoshone Power Plant (hydro-electric) in Glenwood Canyon, CO is the 60hz 'clock' that the Western Power Grid is timed. Meaning that it, Shoshone, is the standard for all the powerplants to sync to.

Any truth to this?

What happens if all the plants on the grid go down? They cannot all just fire up and run power to the grid or, I suppose, a huge physical timing sequence of plants coming on-line in a certain order would be required.

I understand about the atomic clock with the GPS, but it would make sense for a physical plant to be used for phasing and frequency and such. A hydro plant makes most sense as they are rarely off-line and are fairly 'hands-free'.
  #12  
Old 05-24-2012, 12:12 PM
TriPolar is offline
Guest
 
Join Date: Oct 2007
Location: rhode island
Posts: 41,254
Someone will provide an answer in a jiffy.
  #13  
Old 05-24-2012, 08:12 PM
ZenBeam is offline
Guest
 
Join Date: Oct 1999
Location: I'm right here!
Posts: 8,858
So 4 1/2 years on, does anyone have a verifiable reason why they run the frequency slightly fast at night, to "catch up" with the cycles lost during the day, instead of just running at the correct frequency?

Is there an answer to which of these came first?
a) electric clocks rely on the power supply keeping up, which it was already doing for whatever reason
or
b) the power supply makes up the cycles lost during the day, to maintain the accuracy of electric clocks.
  #14  
Old 05-24-2012, 08:59 PM
TriPolar is offline
Guest
 
Join Date: Oct 2007
Location: rhode island
Posts: 41,254
No doubt a) came first. The first electric clocks must have relied on the AC cycle to maintain constant speed, but would have required periodic adjustment. Then, if it is true, the electricity providers would have attempted to keep them accurate by adding/subtracting cycles at night.
  #15  
Old 05-24-2012, 09:06 PM
ZenBeam is offline
Guest
 
Join Date: Oct 1999
Location: I'm right here!
Posts: 8,858
Quote:
Originally Posted by TriPolar View Post
No doubt a) came first. The first electric clocks must have relied on the AC cycle to maintain constant speed, but would have required periodic adjustment. Then, if it is true, the electricity providers would have attempted to keep them accurate by adding/subtracting cycles at night.
You say a) came first, but then your description makes it sound like you think b) came first.
  #16  
Old 05-24-2012, 09:14 PM
TriPolar is offline
Guest
 
Join Date: Oct 2007
Location: rhode island
Posts: 41,254
Quote:
Originally Posted by ZenBeam View Post
You say a) came first, but then your description makes it sound like you think b) came first.
I'm saying the cycles would have been the only practical way to maintain relatively good time with the first AC clocks. It wouldn't have been completely accurate based on variations in the cycle, so eventually, at some later date, the compensation would have been introduced so that electric clocks didn't need to be reset on a regular basis.

Last edited by TriPolar; 05-24-2012 at 09:15 PM.
  #17  
Old 05-24-2012, 10:39 PM
Saintly Loser is offline
Guest
 
Join Date: Aug 2002
Posts: 3,360
Quote:
Originally Posted by Hari Seldon View Post
Let me note that Quebec, like Texas is not connected to any other grid. They sell power to New England and New York, so they must have ways of synching.
As a (very) side issue to this thread, there's a longstanding and very bitter dispute going on between the provinces of Quebec and Newfoundland & Labrador about Quebec's sale of power generated at the Churchill Falls plant in Labrador.

Newfoundlanders feel, very strongly, that they're being robbed to the tune of billions of dollars by Quebec.
  #18  
Old 05-24-2012, 11:12 PM
racer72 is offline
Charter Member
 
Join Date: Mar 2002
Location: Auburn, WA
Posts: 6,446
Just checked an AC outlet in my garage with my trusty Fluke meter. 58.73 Hz. Maybe that's why my electric clocks lose a bit of time each month.
  #19  
Old 05-24-2012, 11:29 PM
johnpost is offline
Guest
 
Join Date: Jul 2009
Posts: 12,056
Quote:
Originally Posted by racer72 View Post
Just checked an AC outlet in my garage with my trusty Fluke meter. 58.73 Hz. Maybe that's why my electric clocks lose a bit of time each month.
periodically measure it and see if it varies.
  #20  
Old 05-25-2012, 07:50 AM
ZenBeam is offline
Guest
 
Join Date: Oct 1999
Location: I'm right here!
Posts: 8,858
Quote:
Originally Posted by racer72 View Post
Just checked an AC outlet in my garage with my trusty Fluke meter. 58.73 Hz. Maybe that's why my electric clocks lose a bit of time each month.
IANAPE (Powergrid Engineer), but that seems unreasonably low to me. Are you on a local generator or something, instead of one of the main grids?
  #21  
Old 05-25-2012, 09:59 AM
hibernicus is offline
Charter Member
 
Join Date: Oct 2000
Location: Dublin, Ireland
Posts: 2,338
Okay, I know something about this, and I can tell you that 58.73 Hz on a large 60 Hz synchronous system is very unlikely, and would represent a dire emergency for the system operator.

I don't know exactly how it's managed in North America, but in Europe it works something like this:
Primary regulation (of frequency) is provided automatically by generating units, which modulate their power output up and down slightly to compensate for small variations (+/-0.2 Hz) in the system frequency. The timescale is of the order of 15 seconds.

Secondary regulation involves generating units being instructed to increase or decrease their power output more substantially, to compensate for a larger frequency excursion. The timescale here is approximately 1.5 minutes.

If this did not happen, a sudden drop in frequency (caused, for example, by the loss of a major generating unit) can cause other generating units in turn to trip, leading to a runaway effect that in the worst case can leave country-sized areas blacked out for long periods. To prevent this, decisive action in the first few seconds is critical.

About the time service, every hour or so, the system operator will adjust the system frequency to try to achieve exactly 50 Hz on average over the day.

And yes, it is still possible to synchronise a generator of any size using light-bulbs without making the earth move, and shift managers still know how to do that.
  #22  
Old 05-25-2012, 11:43 AM
Kevbo is offline
Guest
 
Join Date: May 2005
Posts: 5,917
Quote:
Originally Posted by hibernicus View Post

And yes, it is still possible to synchronise a generator of any size using light-bulbs without making the earth move, and shift managers still know how to do that.

I will second this. It takes perhaps 5 minutes and 2-3 repetitions to teach someone how to do this. The indicator I have used was just two light bulbs. You adjust the speed off line until the pulsing is very slow, and throw the switch when both are off. I think one would work, but two provide redundancy.

It may be that gas turbines, etc do not throttle so nice, and utilities may want them online as quickly as possible, so modern practice may be to "catch" the at-speed, in-phase condition as they ramp up under rather high power input...so computer control may indeed be preferred.

But it is rather trivial to monitor the extant phase of the grid if you want to automate the process: there is never a need to predict the phasing based on absolute timekeeping. That is to say that you have the mother of all phase references connected to any generating station.

As for the Glenwood Canyon plant providing a phase reference for an entire grid, I can't really see how that could work. The frequency/phase of the grid depends on the net mechanical power input at the aggregate of all generators, and the net load on the grid. A big generating station can push the frequency/phase around a little bit, but the Glenwood Canyon plant is fairly small. Small enough that I have seen Kayakers "playing" in the discharge. They are also pretty limited on their ability to control mechanical power input, as that dam contains very little water as such things go. If they tried to run at 2X the inflow rate, the level would probably drop noticeably within 10-20 minutes or so. (total WAG, but I have an engineer's eye, and probably looked at this place at least 100 times over the last 50 years)

Last edited by Kevbo; 05-25-2012 at 11:43 AM.
  #23  
Old 05-25-2012, 12:00 PM
engineer_comp_geek's Avatar
engineer_comp_geek is online now
Robot Mod in Beta Testing
Moderator
 
Join Date: Mar 2001
Location: Pennsylvania
Posts: 25,563
Quote:
Originally Posted by Kevbo View Post
I think one would work, but two provide redundancy.
On a three phase generator you want three bulbs, one for each phase. If they blink out of order you've got your phases out of sequence and you need to switch two of your lines around or very bad things will happen when you throw the switch.

Technically one bulb would work for a single phase or a split single phase generator, but two bulbs gives you a visual indication that you don't have one of your lines and neutral reversed. It's a bit of an idiot check, but it's nice to have (IMHO).
  #24  
Old 05-25-2012, 12:29 PM
engineer_comp_geek's Avatar
engineer_comp_geek is online now
Robot Mod in Beta Testing
Moderator
 
Join Date: Mar 2001
Location: Pennsylvania
Posts: 25,563
Quote:
Originally Posted by Kevbo View Post
As for the Glenwood Canyon plant providing a phase reference for an entire grid, I can't really see how that could work.
I suspect that what they really mean is that Glenwood Canyon is the official time keeper for the system and sends out the commands to all of the other systems to coordinate their generators and get the cycle counts back where they want them.

I know kevbo understands this, but for the benefit of others who might not, here's how generators work.

If you take two generators and tie them together, they hold each other in sync. If you add power to one, it ends up trying to spin the other generator like a motor to get it to catch up to the same frequency, so it gets much more difficult to speed the two generators up. Similarly, if you remove power from one generator, it starts to act like a motor and gets spun by the other generator, making it more difficult to slow the pair down. With more than two generators it gets even worse. If you have ten generators on a line and you remove power from one, the other nine will spin it like a motor, and with that many generators adding power or removing power from one generator has very little effect on the overall line. So, it gets very difficult to speed up or slow down the entire line. You have to coordinate with all of the generators to slightly add or remove power simultaneously.

So speeding up or slowing down the entire "grid" ends up being a coordinated effort between all of the generators on the system. One generator can't directly control the line. Anything that "controls" the overall grid is really sending control commands to each generator to coordinate their actions on the grid.

Quote:
Originally Posted by ZenBeam View Post
So 4 1/2 years on, does anyone have a verifiable reason why they run the frequency slightly fast at night, to "catch up" with the cycles lost during the day, instead of just running at the correct frequency?
Power systems in general are loaded much more heavily during the day, especially on hot days. In the U.S., the northeast and southwest are both close to being overloaded on hot summer days when everyone is running their air conditioning. This is why one little failure in either location can lead to massive blackouts (overloading makes them vulnerable to what is known as a "cascade failure" where since everything is tied together, a fault on one means that the one next to it can't supply enough power to cover the fault and it also trips, causing the one next to it to also trip, and so on and so on in a long cascade of failures).

Since everything is overloaded during the day, this tends to slow down all of the generators at once. So they make up for it by speeding things up a bit at night when the load decreases.

Quote:
Originally Posted by racer72 View Post
Just checked an AC outlet in my garage with my trusty Fluke meter. 58.73 Hz. Maybe that's why my electric clocks lose a bit of time each month.
It may read low during the day and higher at night.

I also thought I read somewhere that they weren't going to maintain the long term frequency like they used to since synchronous clocks aren't used much any more.
  #25  
Old 05-25-2012, 12:36 PM
Darth Panda is offline
Guest
 
Join Date: Mar 2010
Location: NC
Posts: 5,681
Quote:
Originally Posted by ZenBeam View Post
So 4 1/2 years on, does anyone have a verifiable reason why they run the frequency slightly fast at night, to "catch up" with the cycles lost during the day, instead of just running at the correct frequency?
In theory, it would be because power is cheaper and more plentiful at night, as loads are lower. Keeping loads constant, frequency is a function of generation levels. During the day, we have what we call our "peak" hours that require us to ramp up our generation resources, commit less efficient units, etc. At night, we often run into minimum generation constraints, where it is difficult to ramp our generation levels down to the low load levels that occur at night. This often causes utilities to need to "dump" energy at night (selling at a loss). Obviously, you could reduce gen by decommitting units, but if you need those units for the peak of the next day then can be problematic - either expensive (incurring start costs) or sometimes impossible, due to minimum down times or ramp rate constraints.

So, all in all, you have plenty (or more) power at night, and are often just squeaking by during the day, which means that if you wanted to fiddle with frequency a little bit, then running a little short during the day, and a little long during the night would make sense. The reality is that this isn't really done, as the regulations from the NERC are pretty tight, and it's just easier to play it straight. What we do is to continually over or under generate by small amounts, trying to swing back and forth several times per hour (this is easier than trying to nail it, and more efficient).

FWIW, the actual thing we monitor on our trading floor / dispatch desk is ACE, or Area Control Error - we see frequency, but ACE is what we dispatch to.
http://everything2.com/title/Area+Control+Error

Last edited by Darth Panda; 05-25-2012 at 12:40 PM.
  #26  
Old 05-25-2012, 12:50 PM
BubbaDog's Avatar
BubbaDog is offline
Charter Member
 
Join Date: Mar 2003
Location: KC MO or there abouts
Posts: 5,751
Quote:
Originally Posted by ZenBeam View Post
IANAPE (Powergrid Engineer), but that seems unreasonably low to me. Are you on a local generator or something, instead of one of the main grids?
I(Am)APE

My vote is on an error at the Fluke meter or something in the distribution system may be causing a false reading. That frequency is well below where automatic relay systems would shed load in order to bring the frequency back up.

Somewhere around 59.3 the load aggregators are required to shed around 6% of the system load. Below 59.1 Hz another 6%.

Way to much info on this here The table at section 1.1.1 shows frequencies and load percentages.

Basically at 58.73hz about 20% of the load has been shed and generator safety systems are quickly timing out and tripping the generators off line in order to avoid damaging them.

Last edited by BubbaDog; 05-25-2012 at 12:53 PM. Reason: bad number
  #27  
Old 05-25-2012, 12:59 PM
Darth Panda is offline
Guest
 
Join Date: Mar 2010
Location: NC
Posts: 5,681
Quote:
Originally Posted by BubbaDog View Post
I(Am)APE
I thought you(were)Dog.

Last edited by Darth Panda; 05-25-2012 at 12:59 PM.
  #28  
Old 05-25-2012, 05:42 PM
ZenBeam is offline
Guest
 
Join Date: Oct 1999
Location: I'm right here!
Posts: 8,858
Quote:
Originally Posted by engineer_comp_geek View Post
[A bunch of correct stuff deleted...] So they make up for it by speeding things up a bit at night when the load decreases.
But that last sentence just glosses over the question Napier had that's still unanswered. Why do they need to make up for it? Why not just aim for the correct frequency? I don't think Darth Panda's link on Area Control Error answers this either.

Prior to electric clocks, I have to believe people were used to adjusting their clocks often, or at least living with them off by a minute or five. A minute is 3600 cycles, so nailing that number of cycles every day or so seems like overkill.

Quote:
Originally Posted by BubbaDog
My vote is on an error at the Fluke meter or something in the distribution system may be causing a false reading.
I thought of that, but racer72 says his clocks lose time over a month.

(Unless... racer72, these electric clock aren't battery powered, are they? Just checking...)
  #29  
Old 05-25-2012, 06:14 PM
Darth Panda is offline
Guest
 
Join Date: Mar 2010
Location: NC
Posts: 5,681
On rereading ZenBeam's post, I'm changing my post.

Last edited by Darth Panda; 05-25-2012 at 06:18 PM.
  #30  
Old 05-25-2012, 06:19 PM
Darth Panda is offline
Guest
 
Join Date: Mar 2010
Location: NC
Posts: 5,681
Quote:
Originally Posted by ZenBeam View Post
Why not just aim for the correct frequency?
2 parts:

1) We do.
2) Kind of, we swing back and forth about 15 times per hour.

The day-time night-time thing is kind of explained in my post, if you read it carefully. (But to summarize and be more explicit: sometimes we drag during the day, because load is creeping up and we have to chase it. But, in general, we stay pretty flat most of the time).

I'm not hypothesizing - I've spent years working with these guys, the actual dispatchers who run a very, very large US system.

Last edited by Darth Panda; 05-25-2012 at 06:22 PM.
  #31  
Old 05-25-2012, 06:27 PM
Darth Panda is offline
Guest
 
Join Date: Mar 2010
Location: NC
Posts: 5,681
Missed edit window again, sorry.

Next Tuesday, I'll ask our director of dispatch operations if there's anything else that's relevant here.
  #32  
Old 05-25-2012, 08:44 PM
ZenBeam is offline
Guest
 
Join Date: Oct 1999
Location: I'm right here!
Posts: 8,858
Quote:
Originally Posted by Darth Panda View Post
Quote:
Originally Posted by ZenBeam
Why not just aim for the correct frequency?
2 parts:

1) We do.
2) Kind of, we swing back and forth about 15 times per hour.
So the 5184000 cycles per day thing is a myth? Looking at Napier's links supporting the "speed up at night to get to 5184000 cycles every day" theory, they do all seem a little weak. Nothing authoritative, really.


On another note:

Quote:
Originally Posted by BubbaDog View Post
I(Am)APE
Quote:
Originally Posted by Darth Panda View Post
I've spent years working with these guys, the actual dispatchers who run a very, very large US system.
Alright Smarty-pantses. Where were you back in 2008? (OK, Darth Panda gets a bit of a pass for not having joined yet...) Seriously, if you know or can find out anything about that, I'd be interested.

(In the thread linked to by the thread above, I linked to a bunch of pictures that aren't there anymore, but I was playing around with Google Sites then, so they're available here if you're interested.)
  #33  
Old 05-25-2012, 11:02 PM
BubbaDog's Avatar
BubbaDog is offline
Charter Member
 
Join Date: Mar 2003
Location: KC MO or there abouts
Posts: 5,751
Back in the 30's many rural power systems were basically islands of isolated producers and customers. The frequency could have been different from town to town.

You'd probably have to sell your soul to the devil to get the answer.
  #34  
Old 05-26-2012, 12:17 AM
Darth Panda is offline
Guest
 
Join Date: Mar 2010
Location: NC
Posts: 5,681
Quote:
Originally Posted by ZenBeam View Post
So the 5184000 cycles per day thing is a myth? Looking at Napier's links supporting the "speed up at night to get to 5184000 cycles every day" theory, they do all seem a little weak. Nothing authoritative, really.
During a hot day, it's much more likely that you're "dragging," that is your frequency is too low (we're talking small amounts here - the NERC fines the living shit out of us if we don't stay pretty on), than running too hard. If that happens, we'll catch up as soon as we can, which happens to basically be "night." This doesn't happen all that often for us though - but every power system is different, so I can't really speak for other utilities (except for to say that I doubt they like getting fined any more than we do).

So it's not entirely a myth, more of an exaggeration.


Quote:
Originally Posted by ZenBeam View Post
On another note:

Alright Smarty-pantses. Where were you back in 2008? (OK, Darth Panda gets a bit of a pass for not having joined yet...) Seriously, if you know or can find out anything about that, I'd be interested.
I just started with the Company in 08. Like I said, I'll talk to some of my buddies, and one guy in particular, on Tuesday. I assure you I'll find out much, much more than I really want to know.

eta: here is a somewhat comprehensible review of some of the standards: http://www.nerc.com/docs/oc/ps/tutorcps.pdf (warning: pdf)

Last edited by Darth Panda; 05-26-2012 at 12:21 AM.
  #35  
Old 05-26-2012, 09:58 AM
Crafter_Man's Avatar
Crafter_Man is offline
Member
 
Join Date: Apr 1999
Location: Ohio
Posts: 11,492
Quote:
Originally Posted by racer72 View Post
Just checked an AC outlet in my garage with my trusty Fluke meter. 58.73 Hz. Maybe that's why my electric clocks lose a bit of time each month.
But which is more accurate... the grid frequency, or the time base in your meter?
  #36  
Old 05-26-2012, 10:07 AM
Crafter_Man's Avatar
Crafter_Man is offline
Member
 
Join Date: Apr 1999
Location: Ohio
Posts: 11,492
Quote:
Originally Posted by ZenBeam View Post
But that last sentence just glosses over the question Napier had that's still unanswered. Why do they need to make up for it? Why not just aim for the correct frequency?
Well, they do. But it will never be exactly 60 Hz at any instant. It will either be less than 60 Hz (e.g. 59.999234 Hz) or greater than 60 Hz (e.g. 60.0001059 Hz). Furthermore, I would assume any drift in the frequency occurs slowly. Their goal is for the average frequency to be 60.0000000 Hz over a given time span, like 24 hours. To do this, they make small adjustments to the frequency so that the long-term average is 60.0000000 Hz or whatever.

Why do this? Because many instruments use the grid as a frequency reference, and the power company doesn't want any instrument maker to blame them for not providing a good, accurate frequency. It is impossible for the power company to provide a frequency of exactly 60 Hz at every instant, so they do the next best thing: an averge of exactly 60 Hz (or as close as possible to it) over a given time span.

Last edited by Crafter_Man; 05-26-2012 at 10:10 AM.
  #37  
Old 05-26-2012, 10:27 AM
Francis Vaughan is offline
Guest
 
Join Date: Sep 2009
Location: Adelaide, Australia
Posts: 5,077
Quote:
Originally Posted by ZenBeam View Post
Why do they need to make up for it? Why not just aim for the correct frequency?
From a fundamental level, the answer is because it is impossible. With a varying load you must use some form of feedback system to match the power input (ie the power on the shafts of the generators) to that varying load. You either need to be prescient (which is hard for the average engineer that likes to obey the laws of physics) or you need to apply a correction factor to the system in order to vary the power input to the load, the correction being derived from observing the current behaviour. No physical system can adjust instantly, everything takes some delay, and the moment you have delay you are in the realm of feedback systems and stability analysis. Get it wrong and the system will go unstable. So engineers like like nice well damped feedback system that behave nicely. (Very roughly you must ensure that the speed that the feedback system demands the power input change is slower than the speed at which it actually can vary. The actual margin needed is defined mathematically.) In such a system the frequency will naturally hunt above and below the target. When it does this in a nice smooth manner people are happy. They get given a set of bounds that the hunting behaviour must stay within, but as noted, these - of themselves are reasonably wide. If they were much closer the feedback system would be less easy to get stable, and instability is a very bad word around power engineers.

The power generator managers have a slightly more strict goal than just maintaining the frequency within some defined bounds, they have a target integrated frequency - ie the time. So this guides their operation as described above. Basically it provides an additional set of corrective input to the power input control in addition to just hunting for a target frequency. This additional input is subject to the same stability constraints as the main one. Luckily giving them a 24 hour period in which to get there avoids stability issues by a good margin, but in principle it must be considered.

Last edited by Francis Vaughan; 05-26-2012 at 10:28 AM.
  #38  
Old 05-26-2012, 11:58 AM
ZenBeam is offline
Guest
 
Join Date: Oct 1999
Location: I'm right here!
Posts: 8,858
Quote:
Originally Posted by Crafter_Man
It is impossible for the power company to provide a frequency of exactly 60 Hz at every instant, so they do the next best thing: an average of exactly 60 Hz (or as close as possible to it) over a given time span.
I would think minimizing the RMS frequency error would be "the next best thing", not minimizing the average frequency error.

Quote:
Originally Posted by Crafter_Man
Why do this? Because many instruments use the grid as a frequency reference, and the power company doesn't want any instrument maker to blame them for not providing a good, accurate frequency.
Which came first? Instrument makers relying on the number of cycles being correct, or electric power maintaining the correct total number of cycles?

That's if they even do maintain the correct number of cycles, which I'm not sure is the case. Being off by five cycles per day is one part in a million, which is pretty accurate. And if you needed better accuracy, there are (or were) time-keeping radio stations. The Area Control Error equation that Darth Panda linked to is a mix of power error and frequency error. It's not obvious to me that minimizing ACE will necessarily lead to the correct total number of cycles over a span of time. As I said, it's sounding like a myth to me.

Maybe I missed it, but can someone point to an authoritative cite that they do maintain the correct number of cycles over a day?

Quote:
Originally Posted by Francis Vaughan View Post
From a fundamental level, the answer is because it is impossible.
Sigh. It's certainly possible to aim for the correct frequency.

The question, which is surprisingly difficult to get across for whatever reason, is, when you're already off in one direction (say, low), why aim for the correct number of cycles for the day, instead of aiming for the correct frequency, and not worrying about making up those lost cycles? Why isn't the goal to minimize RMS frequency error?
  #39  
Old 05-26-2012, 12:43 PM
Francis Vaughan is offline
Guest
 
Join Date: Sep 2009
Location: Adelaide, Australia
Posts: 5,077
Quote:
Originally Posted by ZenBeam View Post
Sigh. It's certainly possible to aim for the correct frequency.

The question, which is surprisingly difficult to get across for whatever reason, is, when you're already off in one direction (say, low), why aim for the correct number of cycles for the day, instead of aiming for the correct frequency, and not worrying about making up those lost cycles? Why isn't the goal to minimize RMS frequency error?
It is, but the whole point of what I wrote was to point out that this is not the best solution. You can aim, but you can't ever achieve. Just specifying an RMS value does not include a time period over which you will accept it varying. Stability of the control system places a hard bound on how fast you can vary it, and that places a bound on how tight you can pull in the error. The tighter the error bounds on frequency the less and less stable the control system becomes.

You can place constraints on the damping of the feedback loop. A highly damped system will slowly run up to the set frequency, a less damped one will overshoot and drop back, an underdamped one will wobble back and forth.

In the end you seem to be asking - Why bother with time at all? That is different. The error in frequency is allowed wide for good reason. Keeping everyone's clocks in sync a nice to have. The two aren't in conflict, so it is easy to do. Tight frequency control is very hard through to impossible to do.
  #40  
Old 05-26-2012, 12:51 PM
Rico is offline
Screwing the unscrutable.
Moderator
 
Join Date: Mar 1999
Location: Utah's Dixie
Posts: 4,766
Years ago I purchased a turntable for my mobile DJ business. (Yes, Virginia, there were such things as "records" back in the dark ages)

The store had just taken delivery of a whole lot of these direct drive turntables. I got to the job and set up my equipment.

Good damn thing I hadn't bought two of them. The turntable was a 50hz motor and the 60 hz power really screwed up the motor speed. I had to do the whole night on one turntable. Not fun.

I took it back to the store the next day. They couldn't see the problem until I insisted they plug it in and play a record. Turns out the whole batch they got were 50hz motors.

The timing on the power is for a lot more than clocks.
__________________
Everyone is entitled to their own opinions, but not to their own facts.

Proud Member of the SDMB "99'ers"!
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 05:57 PM.

Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2019, vBulletin Solutions, Inc.

Send questions for Cecil Adams to: cecil@straightdope.com

Send comments about this website to: webmaster@straightdope.com

Terms of Use / Privacy Policy

Advertise on the Straight Dope!
(Your direct line to thousands of the smartest, hippest people on the planet, plus a few total dipsticks.)

Copyright 2019 STM Reader, LLC.

 
Copyright © 2017