Gas furnace starts...then stops

Problem started a few days ago. I hear the sound of the furnace starting up, but before the blower comes on, it just stops. It does this every few minutes. I turned the unit off today because I worried about leaving it to do that while I was at work.

Any idea what can be wrong? My husband thought it might be an airflow issue and changed the furnace filter and checked to make sure nothing was blocking the intake vents. Problem still exists. He's convinced he can figure this out on his own but with 2 kids in the house and some pretty cold weather on it's way, I'm convinced we need to call the professionals.
Reply With Quote
Advertisements  
  #2  
Old 10-24-2012, 11:51 AM
Thudlow Boink Thudlow Boink is offline
Charter Member
 
Join Date: May 2000
Location: Lincoln, IL
Posts: 21,918
Is the pilot light lit?
Reply With Quote
  #3  
Old 10-24-2012, 12:00 PM
TriPolar TriPolar is offline
Guest
 
Join Date: Oct 2007
Pilot out. Gas turned off (or empty if you have tanks). Clogged air intake or chimney. Sounds mostly like no gas. Could be a broken thermocouple or other type of sensor.
Reply With Quote
  #4  
Old 10-24-2012, 12:02 PM
Rachellelogram Rachellelogram is offline
Guest
 
Join Date: Oct 2010
I'd check the pilot light first thing. Same thing happened to the gas furnace in the home I'm renting.
Reply With Quote
  #5  
Old 10-24-2012, 12:04 PM
baileygrrrl baileygrrrl is offline
Guest
 
Join Date: Jul 2004
Thanks, I will have my husband check. He's far from a handyman so I hope this is a simple task!
Reply With Quote
  #6  
Old 10-24-2012, 12:08 PM
ftg ftg is offline
Guest
 
Join Date: Feb 2001
I went thru this last winter. The igniter glows, the gas kicks on, the burners fire up ... and then it all shuts down.

There's usually a blinking code visible thru a peep hole that you can look up to see what the problem might be. Lots of possibilities. Bad sensors, lose wires, etc. In my case, the control board was going bad. I could have saved some money and done it myself but I had the HVAC guy do it.

Some time earlier I had a problem where the fan continued running and it was a high-low sensor which was easy to swap out. That part can also cause premature shutdown problems, IIRC.

There's several forums that specialize in home DIY things, including ones for HVAC pros. (You can't post, but you can search them at least via Google.) Look up your model and any codes.
Reply With Quote
  #7  
Old 10-24-2012, 12:15 PM
engineer_comp_geek engineer_comp_geek is offline
Robot Mod in Beta Testing
Moderator
 
Join Date: Mar 2001
Location: Pennsylvania
Posts: 15,250
Could be a bad flame sensor.

Here's a youtube video showing how to check it.
http://www.youtube.com/watch?v=I86joWL66aE

As ftg said though it could be other things. There are plenty of youtube videos showing you how to test various parts.
Reply With Quote
  #8  
Old 10-24-2012, 12:15 PM
Machine Elf Machine Elf is offline
Guest
 
Join Date: Feb 2007
Quote:
Originally Posted by baileygrrrl View Post
Problem started a few days ago. I hear the sound of the furnace starting up, but before the blower comes on, it just stops. It does this every few minutes. I turned the unit off today because I worried about leaving it to do that while I was at work.
There are a few safety devices that have to "greenlight" before a residential gas furnace will deliver heat. Once the thermostat in your living room tells the furnace "we need heat, " the whole sequence goes something like this:


1. Furnace's controller sends power to the flue (exhaust) gas blower.

2. Controller looks for signal from damper that indicates the flue gas blower is indeed working. If no signal, the process shuts down. If there is a signal, the controller allows blower to run for ~30 seconds (to clear out any natural gas that may have leaked into the burner since the last burn), and then proceeds to step 3.

3. Controller turns on power to the gas ignitor. Usually this is a hot-surface ignitor, a little toaster element that glows red hot.

4. Once the ignitor is hot (10 seconds), the controller opens main gas valve. If the ignitor is working, then the gas ignites, and you hear the burners roaring away. At this point the controller is looking for a signal from the flame detector, which would indicate successful ignition. If there's no signal within a few seconds after opening the main gas valve, the controller assumes the burners aren't lit, and it shuts the main gas valve and aborts the whole process. If there is a signal, then the controller figures the burners are lit, and after a ~30-second preheat, it will turn on the main house blower and start delivering heat.

If no signal in #4, then the controller will try again in a few minutes. After several unsuccessful attempts, it will usually stop trying.

I've had problems in the past with the burners getting shut off in step #4 due to a "no flame detected" condition. This is usually caused by one of two things:

1. bad ignitor. They'll only take so many heat cycles before they crack. If you pull the inspection panel off of your furnace and see that the burners really aren't lighting, look around for that igniter (something like this) somewhere near the burners; if it's cracked, it'll probably be obvious. Take it out, call an appliance parts vendor, and see if they have it in stock. When installing the new one, do not touch the ignitor element; your skin oils will result in premature failure.

2. bad flame sensor. If (while you watch) the burners light up and then shut down a few seconds later, then the ignitor is fine, but your flame sensor ain't happy. Often times you can fix this by cleaning them. Try scrubbing it with steel wool or some other fine abrasive, and then reinstalling.

Last edited by Machine Elf; 10-24-2012 at 12:15 PM..
Reply With Quote
  #9  
Old 10-24-2012, 12:35 PM
baileygrrrl baileygrrrl is offline
Guest
 
Join Date: Jul 2004
Thanks for all of the replies. One thing for sure, I am not going to solve this from my office chair

I'll have my husband do a more detailed look tonight. Thank doG for youtube videos and the like. We may not be able to fix it, but at least we might be able to diagnose the problem.
Reply With Quote
  #10  
Old 10-24-2012, 12:40 PM
AllShookDown AllShookDown is offline
Guest
 
Join Date: Sep 2002
My furnace was doing the same thing a few weeks ago. The furnace guys replaced the control board and all is well. They said it had probably gotten fried in a power surge.
Reply With Quote
  #11  
Old 10-24-2012, 02:05 PM
jasg jasg is online now
Charter Member
 
Join Date: Nov 2001
Location: Upper left hand corner
Posts: 3,700
First and cheapest, change filters. If filters are very dirty, the combustion chamber can overheat and the limit switch will kick in and turn the heater off.
Reply With Quote
  #12  
Old 10-24-2012, 02:05 PM
Kimballkid Kimballkid is offline
Guest
 
Join Date: Dec 2011
Quote:
Originally Posted by ftg View Post
There's usually a blinking code visible thru a peep hole that you can look up to see what the problem might be.
Depends on how new it is. If it's more than a few years old, it may not have anything that will display a code.
Reply With Quote
  #13  
Old 10-24-2012, 02:17 PM
Seanette Seanette is offline
Guest
 
Join Date: Aug 2012
I'm siding with "call a professional", on safety grounds. I also hope you have a working CO detector.
Reply With Quote
  #14  
Old 10-24-2012, 02:21 PM
Folly Folly is offline
Guest
 
Join Date: Aug 2004
Quote:
Originally Posted by engineer_comp_geek View Post
Could be a bad flame sensor.
This was my guess just from the thread title.

The part of the sensor extending into the flame is basically just a bar of metal. I was able to fix mine just by sanding off the oxidation/corrosion buildup or whatever the heck the build up was.
Reply With Quote
  #15  
Old 10-24-2012, 02:31 PM
Folly Folly is offline
Guest
 
Join Date: Aug 2004
In fact here's me asking a similar question in 2007.
http://boards.straightdope.com/sdmb/...d.php?t=404867
Reply With Quote
  #16  
Old 10-24-2012, 02:32 PM
Machine Elf Machine Elf is offline
Guest
 
Join Date: Feb 2007
Quote:
Originally Posted by Seanette View Post
I'm siding with "call a professional", on safety grounds. I also hope you have a working CO detector.
Ignitors and flame detectors are easy-to-service items that don't present any particular danger to a homeowner who knows how to use a screwdriver and a circuit breaker.

A particularly smart homeowner will have a spare ignitor handy so that when the in-use one breaks at 9:00 on a Saturday night in January, he doesn't have to wait 36 icy hours to buy a replacement.

As for the CO detector, I concur. Furnace heat exchangers crack and chimneys get blocked from time to time, and as insidious as CO poisoning is, no home should be without a detector.

Last edited by Machine Elf; 10-24-2012 at 02:33 PM..
Reply With Quote
  #17  
Old 10-24-2012, 03:08 PM
johnpost johnpost is offline
Guest
 
Join Date: Jul 2009
Quote:
Originally Posted by Seanette View Post
I'm siding with "call a professional", on safety grounds. I also hope you have a working CO detector.
should have one outside of each bedroom area. also having one near fuel burning heater/boiler/furnaces is good.
Reply With Quote
  #18  
Old 10-24-2012, 08:38 PM
ZipperJJ ZipperJJ is offline
Just Lovely and Delicious
Charter Member
 
Join Date: Aug 2001
Location: Northeast Ohio
Posts: 22,324
Quote:
Originally Posted by engineer_comp_geek View Post
Could be a bad flame sensor.

Here's a youtube video showing how to check it.
http://www.youtube.com/watch?v=I86joWL66aE

As ftg said though it could be other things. There are plenty of youtube videos showing you how to test various parts.
Do this cuz it's free and easy. I do mine once a year now that I know how to do it and it's solved my problem every year so far.

If that doesn't work then call The Man. But don't pay The Man to clean your flame sensor!

I had a cracked somethingorother one year, and the crack would not be a problem until it expanded too much from heat at which point a vacuum was unsealed.
Reply With Quote
  #19  
Old 10-25-2012, 10:40 PM
Tamex Tamex is offline
Guest
 
Join Date: Jul 2000
Quote:
Originally Posted by ZipperJJ View Post
Do this cuz it's free and easy. I do mine once a year now that I know how to do it and it's solved my problem every year so far.

If that doesn't work then call The Man. But don't pay The Man to clean your flame sensor!
This. We've had this very problem, and it's always been the flame sensor. Had to call The Man to fix it once (in the middle of winter, of course!) but after that, my husband has always cleaned it himself.
Reply With Quote
  #20  
Old 01-15-2014, 08:00 AM
c46443 c46443 is offline
Guest
 
Join Date: Jan 2014
One last possible solutin

Before calling out a repairperson, after you have checked the pilot light, cleaned the flame detector and all the wire connections, the last item to check would be the small air hose lines that sense the air flow in the furnace. Unplug each end and check for dust clogs anywhere. I used a wet vac to suck out all the dust when my furnace had the same problem and fixed the furnace. The last and most expensive is replacing the control board.
Reply With Quote
  #21  
Old 01-15-2014, 08:32 AM
DCnDC DCnDC is offline
Guest
 
Join Date: Feb 2010
Check the date on the OP. It's been well over a year. Hopefully her problem has been fixed by now.
Reply With Quote
  #22  
Old 01-15-2014, 09:13 AM
Amateur Barbarian Amateur Barbarian is offline
Guest
 
Join Date: Apr 1999
All of the above is true, but I've also had gas furnaces do this short-cycle thing when the thermostat did not have an adequate temperature hysteresis - there should be a degree or more between the temp it turns on and the temp it turns off. If the band is too narrow, it will jitter between on and off until the house temp drops another degree or so. The test is to force the furnace on by turning the thermostat up several degrees - if the furnace kicks on and runs fine, replace the thermostat.

Last edited by Amateur Barbarian; 01-15-2014 at 09:13 AM..
Reply With Quote
  #23  
Old 02-06-2014, 06:22 PM
andrewclaus andrewclaus is offline
Guest
 
Join Date: Feb 2014
Similar furnace lighting problem

I thought I'd piggyback on this old thread with a similar problem. I have a cheap Goodman furnace in a rental house that just had an ignitor fail. I replaced the ignitor and now I notice it takes two cycles to fire. The new ignitor glows just fine, but only for a second or two before the gas valve opens. The first time it doesn't light and shuts down. The second cycle, the same thing happens but the burners ignite. I thought the ignitor was supposed to glow for much longer before the gas valve turns on.

I don't know if this was happening before the ignitor replacement. Could it have anything to do with that? Is there an adjustment for this, should I get a new control board, or any other ideas?

Thank you. This is my first post here and I'm impressed with the replies above.
Reply With Quote
  #24  
Old 05-10-2016, 09:47 AM
caoboys caoboys is offline
Guest
 
Join Date: May 2016
Hi All,

I am having almost the same problem:

when the heater starts, I can see the gas blower starts, then the gas starts burning - the burners roaring away for about 30 second or a minutes then the burner stops before the main house blower starts. So when the main blower run, it just blow the cold air (without heat) so the processes keep doing over and over. If I turn off the heater from thermostat and turn off the main furnace power completely then turn the eater back on again then the heater will run as normal for several cycle then repeat the same problem. I would like to replace the board controller but just want to make sure if it is the right thing to do. Any help would appreciated.

Thank you-
Reply With Quote
  #25  
Old 05-10-2016, 05:35 PM
I. Dunno I. Dunno is online now
Guest
 
Join Date: Nov 2014
Quote:
Originally Posted by caoboys View Post
Hi All,

I am having almost the same problem:

when the heater starts, I can see the gas blower starts, then the gas starts burning - the burners roaring away for about 30 second or a minutes then the burner stops before the main house blower starts. So when the main blower run, it just blow the cold air (without heat) so the processes keep doing over and over. If I turn off the heater from thermostat and turn off the main furnace power completely then turn the eater back on again then the heater will run as normal for several cycle then repeat the same problem. I would like to replace the board controller but just want to make sure if it is the right thing to do. Any help would appreciated.

Thank you-
Get the make and model number of the board and do an internet search and see if you can find a sequence of operation for the board. A sequence of operation will give the timings of the various components as they start and run.

In other words, first the thermostat calls for heat. The induction blower and the igniter are energized. X number of seconds later, (usually 15-30), the main valve is opened and the burners ignite. X number of seconds after that, perhaps 30-60, the blower will start. See if your furnace is operating as it should.

I'm wondering if the high limit is opening and shutting down the burners. Either because it's defective or because the board itself may not be starting the blower in time. Or possibly my experience below.

My furnace, a couple of winters ago, was doing something similar to what you describe. In my case, the capacitor was bad on the blower motor and the fan didn't start when it should have. High limit shut off the gas and the unit would attempt a restart. It would apparently work some of the time or at least the second time because the house never got cold and it ran half the winter before I discovered there was even a problem. (I happened to be in the basement one evening when it shut down and then ran properly the second time.)

I'm a retired HVAC tech and I thought it was the board gone bad. I put in a spare I had but that didn't help. Eventually I put a meter on the capacitor and found the problem.

It's not likely that's whats wrong with yours, but it's something to consider.
Reply With Quote
  #26  
Old 05-12-2016, 09:15 AM
caoboys caoboys is offline
Guest
 
Join Date: May 2016
Thank you Dunno ! I tried to reset the power again last night but it did not work like it used to be - I meant for the last couple months, everytime I reset the power, the heater will run as it suppose to for several cycles but now, the burner stopped before the main blower start - it seems like the blower working fine - the only thing is I don't know if the flame sensor bad or the whole board but I think this is a good time to replace the board control - unless there is a better way to troubleshoot to isolate the problems.

Thank you-
Reply With Quote
  #27  
Old 05-12-2016, 11:27 AM
I. Dunno I. Dunno is online now
Guest
 
Join Date: Nov 2014
Quote:
Originally Posted by caoboys View Post
Thank you Dunno ! I tried to reset the power again last night but it did not work like it used to be - I meant for the last couple months, everytime I reset the power, the heater will run as it suppose to for several cycles but now, the burner stopped before the main blower start - it seems like the blower working fine - the only thing is I don't know if the flame sensor bad or the whole board but I think this is a good time to replace the board control - unless there is a better way to troubleshoot to isolate the problems.

Thank you-
It's hard for me to troubleshoot from this distance, but it may very well be the board. Also could be the flame sensor. Have you tried cleaning it? Sometimes helps.

And like I said above, it COULD be that the blower is coming on too late, causing the burner to go out on the high limit. How long does the burner stay lit?
Reply With Quote
  #28  
Old 05-12-2016, 10:15 PM
usedtobe usedtobe is offline
Guest
 
Join Date: Jul 2008
Does the unit have self-diagnosis?

Is it flashing a code?

Can you switch the fan to "on" (instead of "auto") - does the blower (air mover) come on and stay on?
Reply With Quote
  #29  
Old 05-15-2016, 03:43 PM
sghokie sghokie is offline
Guest
 
Join Date: May 2016
My furnace just experienced a flame sensor problem plus another problem.

It was kicking on then off after a few seconds, so I cleaned the flame sensor, it would run for a little longer then turn off. So I ordered a new flame sensor. Put it in, same thing, on for about 30 seconds then off.

I did some head scratching and eventually decided to pull off the hose from the pressure switch after it kicked off. The end of the hose was loose and also warm.
So I pressed it on tighter, problem solved.
Reply With Quote
  #30  
Old 05-15-2016, 05:59 PM
Oddball_92 Oddball_92 is offline
Guest
 
Join Date: Jan 2013
Since this was originally posted in 2012, I expect it is fixed by now.

Last edited by Oddball_92; 05-15-2016 at 05:59 PM..
Reply With Quote
  #31  
Old 05-16-2016, 12:45 AM
I. Dunno I. Dunno is online now
Guest
 
Join Date: Nov 2014
Quote:
Originally Posted by Oddball_92 View Post
Since this was originally posted in 2012, I expect it is fixed by now.
We are trying to help caoboys who posted in this thread with a furnace problem this week. I'm aware it's a zombie but evidently you didn't read through the whole thing.
Reply With Quote
Reply



Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 11:55 PM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2016, vBulletin Solutions, Inc.

Send questions for Cecil Adams to: cecil@chicagoreader.com

Send comments about this website to: webmaster@straightdope.com

Terms of Use / Privacy Policy

Advertise on the Straight Dope!
(Your direct line to thousands of the smartest, hippest people on the planet, plus a few total dipsticks.)

Publishers - interested in subscribing to the Straight Dope?
Write to: sdsubscriptions@chicagoreader.com.

Copyright 2015 Sun-Times Media, LLC.