Electrical Fire Questions and a Thank you

First, I'd like to thank those who responded to my inquiries about plugs being left slightly, well, ajar in the the outlet (that is, half inserted) and their potential to cause fire. I now know that the risk is minimal at best and that is only with high loads (1000W+). Reading the responses about it had greatly reduced my OCD on the matter to a point where it doesn't really obstruct my life. That being said, I still am curious about something related to it. Here goes:

When I was freaking out about it I did google searches on it and absolutely could NOT find any statistics about how fires could be caused from a plug being halfway inserted, I looked everywhere and there was no mention of fires caused by it. I know that it is possible.
Is it really that miniscule of a risk that it is not even mentioned? or is it that it may be lumped into a category of other electrical fires/home fires?

I figured that some insurance company somewhere would have statistics on it but the only thing related was if the outlet was wired incorrectly. Any insight into this would be nice. Also I am curious, do AFCI breakers trip if you, lets say have a vacuum plugged in and pull the plug while it's still 'on' and it creates a little tiny blue spark at the outlet from the load?

Thanks again. All of you are the best.
Advertisements  
  #2  
Old 03-12-2017, 08:56 PM
beowulff beowulff is offline
Member
 
Join Date: May 2001
Location: Scottsdale, more-or-less
Posts: 14,819
You really need to let this go.

IMHO, it's probably very, very hard for a fire investigator to determine how far out of the socket a plug was when it's been in a fire. They would most likely just lump it into a generalized "overloaded circuit" category. As for AFCI, they have a microcontroller inside of them which is supposed to be able to tell the difference between normal plug-disconnect sparks and real faults. Like any device, there is nuisance tripping.
  #3  
Old 03-12-2017, 09:01 PM
Weisshund Weisshund is offline
Guest
 
Join Date: Dec 2016
Posts: 1,601
I think it is going to depend a lot on the condition of the outlet, and what is plugged into it.

Average household items, most likely will just ruin the plug and outlet from constant arching.
If the outlet fits good, possibly nothing happens, if its an old worn loose outlet, it might arc and burn up the contacts.

Best practice if to plug them all the way in, then they dont fall out or get bent or arc

I do not know if unplugging the vacuum will trip an AFCI protected outlet, i suppose it could being that an electric motor will usually make a decent little arc if it is unplugged while running.
  #4  
Old 03-12-2017, 09:17 PM
Princhester Princhester is offline
Charter Member
 
Join Date: Jan 2001
Location: Brisbane, Australia
Posts: 14,257
Quote:
Originally Posted by beowulff View Post
IMHO, it's probably very, very hard for a fire investigator to determine how far out of the socket a plug was when it's been in a fire. They would most likely just lump it into a generalized "overloaded circuit" category.
I don't think this is correct. Arcing produces very distinct patterns on metal contacts. The patterns typically survive the fire because the temperature of a house fire is usually lower than the temperature necessary to melt the metal. There is a very good chance that a fire investigator could tell that a plug was not properly inserted because they would find the arc points, and the arc points would be at the very tip of the contacts. If the plug and socket weren't the cause of the fire they won't show signs of arcing. And a properly inserted plug isn't likely to undergo arcing even if it is subject to overload (something else will fail first) but even if it is, the arcing would be mid-contact, not at the very tips.
  #5  
Old 03-12-2017, 09:26 PM
Crazyhorse Crazyhorse is offline
Guest
 
Join Date: Sep 2008
Posts: 3,036
Well, here's one alleged example: https://fire9prevention.wordpress.co...n-all-the-way/

I'm not familiar with the previous thread mentioned and I'm sure there is some good information in there, but in general plugging something in halfway certainly could create the potential for fire.

Quote:
Originally Posted by Princhester View Post
I don't think this is correct. Arcing produces very distinct patterns on metal contacts. The patterns typically survive the fire because the temperature of a house fire is usually lower than the temperature necessary to melt the metal. There is a very good chance that a fire investigator could tell that a plug was not properly inserted because they would find the arc points, and the arc points would be at the very tip of the contacts. If the plug and socket weren't the cause of the fire they won't show signs of arcing. And a properly inserted plug isn't likely to undergo arcing even if it is subject to overload (something else will fail first) but even if it is, the arcing would be mid-contact, not at the very tips.
According to this 50-75% of all home electrical fires in the US are caused by arc faults. Obviously these are usually from more serious and permanent arcs than caused by a jiggling a halfway-connected power cable but there is that potential anytime you ever see a spark.

They classify electrical fires by the appliance they started in and not by the actual cause so this isn't obvious by viewing reports and statistics.

Quote:
Two recent reports – one from the National
Fire Protection Agency (NFPA)a and one from
the National Association of State Fire Marshals
(NASFM)b – estimate that 50 to 75 percent of
all electrical home fires in the United States
are caused by arc fault conditions. Data from
the National Fire Incident Reporting System
and the NFPA, meanwhile, indicate that
between 1994 and 1998, electrical arcing
caused approximately 48,800 fires annually in
one- and two-family dwellings.

If these statistics surprise you, you are not
alone. Even many electrical professionals do
not realize the true extent of arcing-related
fires because the real culprit can be hidden
by the reporting categories used to classify
fires. These classifications, which include
categories such as heating, cooking, electrical
distribution, appliances, light fixtures,
electronic/office, and “other equipment,” tend
to point to the places where the fires originate
rather than to what caused them. Increasingly,
however, experts are realizing that many of
these categories trace back to a single source:
arc faults.

Last edited by Crazyhorse; 03-12-2017 at 09:28 PM.
  #6  
Old 03-12-2017, 09:55 PM
anomalous1 anomalous1 is offline
Guest
 
Join Date: Jan 2017
Location: Chicago, IL
Posts: 746
This

Exactly this, I must have somehow missed that article but it is pretty concise, even states there is overlap on the conditions that can cause it. Thanks Crazyhorse

Beowulff I agree, I am pretty much over it, but the fact that it was never directly attributed, or at least in writing from what I've found, was bothering me. Glad to know about the controller that can tell the difference, Thanks!

Weisshund Thanks, I've yet to have it happen, but I just want to know if it will ever become a nuisance, I suppose I could use the excercise to run up and down to hit the breaker, but I hope not. Thank you!

I know that the general consensus here is that a half inserted plug isn't a great fire risk(especially with nothing combustible around), I got that from my previous posts too. Even if nominally past the OCD with the subject, I still have curiosity about it.
  #7  
Old 03-13-2017, 06:08 AM
Crafter_Man Crafter_Man is offline
Guest
 
Join Date: Apr 1999
Location: Ohio
Posts: 10,392
Quote:
Originally Posted by Princhester View Post
I don't think this is correct. Arcing produces very distinct patterns on metal contacts. The patterns typically survive the fire because the temperature of a house fire is usually lower than the temperature necessary to melt the metal. There is a very good chance that a fire investigator could tell that a plug was not properly inserted because they would find the arc points, and the arc points would be at the very tip of the contacts. If the plug and socket weren't the cause of the fire they won't show signs of arcing. And a properly inserted plug isn't likely to undergo arcing even if it is subject to overload (something else will fail first) but even if it is, the arcing would be mid-contact, not at the very tips.
Well, as someone who does this for a living...

A plug that is making a poor connection would be creating a series arc. While the temperature of the arc is high, the energy is fairly low, and the telltale signatures of arcing (arc beads, material transfer, etc.) can be difficult to detect. And that is assuming nothing else "bad" has happened. But a series arc usually causes a parallel arc, and thereby destroys all the evidence of the series arc.

This is what normally happens:

1) Series arcing due to a poor contact. This is usually caused by a loose connection where a copper wire wraps around the underside of a screw head. Though it could also be caused by a poor plug/socket connection.

2) A glowing contact might be created by the series arc.

3) Things around the arc (mainly polymers) get very hot.

4) Things around the arc will burn, melt, or char depending on their chemistry.

5) The melting and charing will often eventually create a parallel arc (and thereby plasma).

6) A parallel arc is very high energy. There will be positive feedback and all hell will break loose. (And the circuit breaker may or may not trip at this point.)

The innards of the receptacle will likely look like a piece of charcoal.

So yea, it's possible a failure could occur "just right" such that there are nice arc beads and evidence of metal transfer at the plug/receptacle interface. But more often-than-not it's just a big, molten mess.
  #8  
Old 03-13-2017, 06:02 PM
anomalous1 anomalous1 is offline
Guest
 
Join Date: Jan 2017
Location: Chicago, IL
Posts: 746
Crafter_Man

Thank you, that is exactly the explanation I was looking for, and I can assume from it being a molten mess that its why there are no statistics specifically looking for such a thing as a plug being half out of the socket. But even then the risk is only really there if its a high load device, correct?

Thanks,

J
  #9  
Old 03-13-2017, 07:23 PM
engineer_comp_geek engineer_comp_geek is offline
Robot Mod in Beta Testing
Moderator
 
Join Date: Mar 2001
Location: Pennsylvania
Posts: 19,318
That type of failure is probably going to be lumped under plug/socket failures in the statistics.

A plug that is half out of the socket is probably still going to make good enough contact that it's not a problem, even at high loads. You're only going to have a problem with plugs that are almost completely out of the socket and are just barely hanging on. You have to reduce the contact area between the plug and socket significantly in order to have a potential problem.

I personally have never seen this be a problem. I have however seen connection problems with old (as in 50 to 60 years old or older) sockets where metal fatigue and corrosion have caused them to make poor contact with the plug. If your home has old two-wire sockets and they are original to the house, you should probably replace them (IMHO).

And yes, you are correct that generally you need a significant amount of current flowing though the poor connection in order to get a significant amount of heat generated. Technically, a small amount of current going through a very tiny point of contact can also get pretty hot, but with that you don't have as much overall heat and it's not anywhere near as likely to cause a fire.
  #10  
Old 03-13-2017, 11:11 PM
Princhester Princhester is offline
Charter Member
 
Join Date: Jan 2001
Location: Brisbane, Australia
Posts: 14,257
Quote:
Originally Posted by Crafter_Man View Post
5) The melting and charing will often eventually create a parallel arc (and thereby plasma).
What's a parallel arc? Do you simply mean arcing in several spots at once?
  #11  
Old 03-14-2017, 02:38 AM
anomalous1 anomalous1 is offline
Guest
 
Join Date: Jan 2017
Location: Chicago, IL
Posts: 746
Yep

Yeah, thats what I figured with it being high load and poor connection, and yeah I figured as much that it would be lumped into the same category as other fires. Thanks! My curiosity has been fulfilled.
  #12  
Old 03-14-2017, 05:31 AM
Melbourne Melbourne is offline
Guest
 
Join Date: Nov 2009
Posts: 3,189
Quote:
Originally Posted by Princhester View Post
What's a parallel arc? Do you simply mean arcing in several spots at once?
A parallel arc is in parallel with the load/switch. It's not limited by the load / switch. It's a short circuit. The energy dissipated in the arc and wiring is much greater than the energy you can get when it's in series with something plugged into the outlet.
  #13  
Old 03-14-2017, 06:26 AM
Crafter_Man Crafter_Man is offline
Guest
 
Join Date: Apr 1999
Location: Ohio
Posts: 10,392
Quote:
Originally Posted by engineer_comp_geek View Post
A plug that is half out of the socket is probably still going to make good enough contact that it's not a problem, even at high loads. You're only going to have a problem with plugs that are almost completely out of the socket and are just barely hanging on. You have to reduce the contact area between the plug and socket significantly in order to have a potential problem.

I personally have never seen this be a problem. I have however seen connection problems with old (as in 50 to 60 years old or older) sockets where metal fatigue and corrosion have caused them to make poor contact with the plug. If your home has old two-wire sockets and they are original to the house, you should probably replace them (IMHO).
I would agree that it's pretty rare for a failure to occur at the spring contacts. With receptacles and switches, the primarily problem is the copper wire that is compressed under the screw head (as I noted above). There is no mechanical spring, and you're relying on compression forces. A loose connection will cause arcing and a glowing contact. (Google "glowing contacts" and "Eaton" for more info.)

Quote:
Originally Posted by engineer_comp_geek View Post
generally you need a significant amount of current flowing though the poor connection in order to get a significant amount of heat generated. Technically, a small amount of current going through a very tiny point of contact can also get pretty hot, but with that you don't have as much overall heat and it's not anywhere near as likely to cause a fire.
While heat generated due to insufficient contact area can certainly lead to problems, the most serious issue with contacts is arcing.
  #14  
Old 03-14-2017, 06:34 AM
Crafter_Man Crafter_Man is offline
Guest
 
Join Date: Apr 1999
Location: Ohio
Posts: 10,392
Quote:
Originally Posted by Melbourne View Post
A parallel arc is in parallel with the load/switch. It's not limited by the load / switch. It's a short circuit. The energy dissipated in the arc and wiring is much greater than the energy you can get when it's in series with something plugged into the outlet.
Correct.

As a root cause of a failure, series arcing is much more common than parallel arcing. Furthermore, a standard circuit breaker couldn't care less about series arcing; it won't trip. Meanwhile, the series arc is at an extremely high temperature (thousands of degrees), and things around it will vaporize, burn, melt, char, etc. When hot things vaporize a plasma is formed, and a plasma is electrically conductive. And when things char they also tend to become conductive. These "conductive things" bridge the gap between hot and neutral/ground, and eventually intermittent shorts occur between hot and neutral/ground, often accompanied by lots of sputtering & parallel arcing.
  #15  
Old 03-14-2017, 09:32 AM
Sicks Ate Sicks Ate is offline
Guest
 
Join Date: Feb 2011
Location: KS, US
Posts: 5,423
Quick question: I observed that trimming the neutral wire not connected to a fixture, when (key info here) the hot wire for said fixture is disconnected at the junction box, caused the AFCI breaker to trip. What type of fault was it detecting?
  #16  
Old 03-14-2017, 06:38 PM
Princhester Princhester is offline
Charter Member
 
Join Date: Jan 2001
Location: Brisbane, Australia
Posts: 14,257
Quote:
Originally Posted by Crafter_Man View Post
Correct.

As a root cause of a failure, series arcing is much more common than parallel arcing. Furthermore, a standard circuit breaker couldn't care less about series arcing; it won't trip. Meanwhile, the series arc is at an extremely high temperature (thousands of degrees), and things around it will vaporize, burn, melt, char, etc. When hot things vaporize a plasma is formed, and a plasma is electrically conductive. And when things char they also tend to become conductive. These "conductive things" bridge the gap between hot and neutral/ground, and eventually intermittent shorts occur between hot and neutral/ground, often accompanied by lots of sputtering & parallel arcing.
Interesting. I have quite a lot of experience with vehicle fires, and I suppose the style of wiring (single wire, vehicle body as earth) and the voltage being much lower makes things different.
  #17  
Old 03-14-2017, 07:03 PM
igor frankensteen igor frankensteen is offline
Guest
 
Join Date: Sep 2016
Posts: 1,111
I'm just a lower level repair tech and historian, so I have more basic concerns about this.

I see that no one mentioned the most obvious concern about things plugged in half way: the plug tips are contacting the live socket points, and carrying the voltages and potential current out to where things in the room could contact it. It's essentially like having a pair of bare, live wires hanging out of the socket, instead of being recessed. Still not likely to cause fires, unless something conductive touches them.

Another rather basic thing to realize, is that electricity doesn't flow like water. It doesn't spill out of the socket like water from a spigot. It has to be actively drawn out, so to speak. Something has to ground the hot wire,for current to flow. Even an exposed hot wire wont cause any problems, as long as nothing grounds it.

I was taught when installing outlets, to put them in so that the ground socket (the round one) is on top. The idea is to add a small extra help, in case someone DOES pull a plug half way out, and a metal object chances to fall onto the exposed plug contacts. With the ground on top, the object would fall off, rather than close the circuit between the two lower live wires.
  #18  
Old 03-14-2017, 07:25 PM
bob++ bob++ is offline
Guest
 
Join Date: Jan 2013
Location: Worcestershire UK
Posts: 5,393
Due to the design, we don't have a problem with plugs half out of the socket, but I did once have a problem with a bad connection.

My dishwasher is under the counter, and it is plugged into a socket above the counter. All domestic appliances here come with a moulded plug attached, but I cut that off as I had to thread the cable through a small hole. I fitted a new plug and the machine worked fine.

The socket was a dual type and one day I was plugging something else in and burned my hand on the dishwasher plug. I turned it off and opened it up, to fund that the clown (me) who had wired the plug had not tightened the screw holding the hot wire . This was making a poor contact and was, presumably, glowing red hot when under load. The plug is made of some fire retardant plastic, but the inside was quite melted.
  #19  
Old 03-14-2017, 07:28 PM
Crafter_Man Crafter_Man is offline
Guest
 
Join Date: Apr 1999
Location: Ohio
Posts: 10,392
Quote:
Originally Posted by Princhester View Post
Interesting. I have quite a lot of experience with vehicle fires, and I suppose the style of wiring (single wire, vehicle body as earth) and the voltage being much lower makes things different.
All else being equal, a DC arc is much nastier than an AC arc.

Having said that, I'm pretty sure electrical arcing in an automobile's electrical system is not much of a fire risk as I do not think an arc can be sustained at 12 V to 14 V. This paper seems to agree, assuming I am interpreting it correctly.
  #20  
Old 03-14-2017, 07:37 PM
Crafter_Man Crafter_Man is offline
Guest
 
Join Date: Apr 1999
Location: Ohio
Posts: 10,392
Quote:
Originally Posted by bob++ View Post
The socket was a dual type and one day I was plugging something else in and burned my hand on the dishwasher plug. I turned it off and opened it up, to fund that the clown (me) who had wired the plug had not tightened the screw holding the hot wire . This was making a poor contact and was, presumably, glowing red hot when under load. The plug is made of some fire retardant plastic, but the inside was quite melted.
A couple of things (or both) could have occured:

1) A reduced contact area will increase the current density at the contact area. This will cause the temperature of the contact area to become very high due to I2R heating. In some cases, however, the problem automatically "fixes" itself, at least temporarily. This is because the conductor materials (usually copper) will soften when the get hot, thereby increasing the contact area and thus reducing the temperature. It's negative feedback. But it should be stated that this only occurs when there is a force compressing the terminals together.

2) A poor contact can become a glowing contact. When this happens, a red-hot, moving filament will be created between the two terminals. Eaton Corporation has done quite a bit of research on this topic.
  #21  
Old 03-14-2017, 07:46 PM
Melbourne Melbourne is offline
Guest
 
Join Date: Nov 2009
Posts: 3,189
Quote:
Originally Posted by Crafter_Man View Post
All else being equal, a DC arc is much nastier than an AC arc.

Having said that, I'm pretty sure electrical arcing in an automobile's electrical system is not much of a fire risk as I do not think an arc can be sustained at 12 V to 14 V. This paper seems to agree, assuming I am interpreting it correctly.
??? talking about "stable" arc in air, "0.125 to 48 in, the arc voltages averaged 34 V/in " (0.32 to 122 cm, 13.4 V/cm)

That's 3 volts at a 10th of an inch. (And you can weld with a 12V solar panel). I think there is a lower limit, a width below which you can't maintain an arc in air, because of the ionization behaviour of air, but it's at less than 3V / eighth of an inch.

Last edited by Melbourne; 03-14-2017 at 07:46 PM.
  #22  
Old 03-14-2017, 08:37 PM
Crafter_Man Crafter_Man is offline
Guest
 
Join Date: Apr 1999
Location: Ohio
Posts: 10,392
Quote:
Originally Posted by Melbourne View Post
??? talking about "stable" arc in air, "0.125 to 48 in, the arc voltages averaged 34 V/in " (0.32 to 122 cm, 13.4 V/cm)

That's 3 volts at a 10th of an inch. (And you can weld with a 12V solar panel). I think there is a lower limit, a width below which you can't maintain an arc in air, because of the ionization behaviour of air, but it's at less than 3V / eighth of an inch.
You may be correct. But the equations suggest a lower limit of about 20 V with a 1 mm width.

I have always wondered about the definitive answer to this question.
  #23  
Old 03-15-2017, 03:00 AM
SamuelA SamuelA is offline
Guest
 
Join Date: Feb 2017
Posts: 1,229
So, back to the OP. I've noticed that if you buy brand new GFCI receptacles, the receptacles have a far more solid feel than the $0.60 home depot special receptacles. It takes a lot more insertion force, and once you plug the device in, there's a lot more force needed to pull the plug back out. The plug won't rattle as much, either.

So as far as I can tell, there's only 2 reasons the OP might have this "half plugged in" problem. Either it's worn out receptacles (I replaced a half dozen in my house this year when I went around doing the GFCI upgrade), or something has too short of a cord.

Either needs replacing. Worn out receptacles don't make just "half contact". Many times they are in such poor condition there's 1/10 the contact area or it's just hanging on by an electrical arc. I found old receptacles where if you plug something in, it'll just hang loose and you have to jiggle the plug to even get power to the device at all. Terrible, and I bet there's a series arc in there sometimes when this happens.

Just buy the slightly higher grade this time. Get the $3-$5 commercial grade receptacles or at least the "Preferred" residential grade that cost about $1.50. The commercial grade ones are a whole different quality tier, they are far heavier and you can just tell they mean serious business.

Last edited by SamuelA; 03-15-2017 at 03:03 AM.
  #24  
Old 03-15-2017, 03:08 AM
SamuelA SamuelA is offline
Guest
 
Join Date: Feb 2017
Posts: 1,229
Oh, one note : if you do decide to replace some faulty receptacles, you should replace with tamper resistant receptacles. Those can save small children from shock when they play with paperclips (I did this and while I didn't die, I could have) and you should also replace some of them with GFCI if the place doesn't have it. The GFCI ones need to be upstream and they can protect everything downstream if wired in correctly. (the instruction packet that comes with each receptacle basically tells you how to do it)


One final note : if you go around replacing receptacles, make sure the power is off! Plug a test device into the receptacle (a lamp or radio) and make sure it comes on. (so you know the test device isn't faulty). Turn off/on breakers until the device turns off. (a radio helps if you don't have an assistant). Leave that breaker off!

For extra paranoia, check with a voltage tester or I put a screwdriver blade between the hot wire and ground. Better to get an arc flash than to get shocked.

Last edited by SamuelA; 03-15-2017 at 03:11 AM.
  #25  
Old 03-15-2017, 03:32 PM
Melbourne Melbourne is offline
Guest
 
Join Date: Nov 2009
Posts: 3,189
Quote:
Originally Posted by Crafter_Man View Post
You may be correct. But the equations suggest a lower limit of about 20 V with a 1 mm width.

I have always wondered about the definitive answer to this question.
I think you will find that the voltage drops in the region 1mm - 4mm. (Or rises in the region 4mm-1mm...)

Also, it depends on the gas (air), humidity, confinement, surface material.

And, regarding the OP, arcing across a surface (tracking) is different again.
  #26  
Old 03-16-2017, 12:10 AM
Princhester Princhester is offline
Charter Member
 
Join Date: Jan 2001
Location: Brisbane, Australia
Posts: 14,257
Quote:
Originally Posted by Crafter_Man View Post
Having said that, I'm pretty sure electrical arcing in an automobile's electrical system is not much of a fire risk as I do not think an arc can be sustained at 12 V to 14 V. This paper seems to agree, assuming I am interpreting it correctly.
Hell no, electrical arcs are the number one source of car and truck fires.

http://hartwood.com.au/wp-content/up...Catch-Fire.pdf
  #27  
Old 03-16-2017, 11:59 AM
Crafter_Man Crafter_Man is offline
Guest
 
Join Date: Apr 1999
Location: Ohio
Posts: 10,392
Quote:
Originally Posted by Princhester View Post
Hell no, electrical arcs are the number one source of car and truck fires.

http://hartwood.com.au/wp-content/up...Catch-Fire.pdf
Excellent find, thank you! So I take back what I said. Well, sort of... I am still pretty sure you can't get a sustained arc at 12 V to 14 V. But you can certainly get an intermittent/sputtering arc at those voltage levels which will produce damage.

(As a side note, virtually all my experience in arc-related failures is for systems operating at 115 V / 400 Hz or 270 VDC. The latter in particular can produce some very impressive arcs. And sustainable ones at that. I don't have any experience w/ automotive arcs.)
  #28  
Old 03-16-2017, 12:18 PM
SamuelA SamuelA is offline
Guest
 
Join Date: Feb 2017
Posts: 1,229
Quote:
Originally Posted by Crafter_Man View Post
(As a side note, virtually all my experience in arc-related failures is for systems operating at 115 V / 400 Hz or 270 VDC. The latter in particular can produce some very impressive arcs. And sustainable ones at that. I don't have any experience w/ automotive arcs.)
So we do agree that the OP needs to replace his or her receptacles. And stop using the broken ones until replacement, right? If the plug won't stay in, it's hanging loose. The blade is not necessarily halfway in contact with the receptacle metal, the very tip could be in contact.

Since it's loose in the receptacle, it's possible for it to just barely make contact well enough to get current moving, and then once the flow is established, if the plug moves just enough, an electrical arc will form. Probably series since probably just 1 prong will be loose enough. And then there's heating and maybe a fire.

On a day to day basis, you won't see that. It's a statistical phenomenon. Out of every bad receptacle with a loose plug in the USA, only a small percent start fires at any moment. Still not a safe situation.
  #29  
Old 03-16-2017, 12:52 PM
Crafter_Man Crafter_Man is offline
Guest
 
Join Date: Apr 1999
Location: Ohio
Posts: 10,392
120 VAC receptacles are very cheap and very easy to replace. If you suspect there is any problem with a receptacle, you should simply replace it ASAP.
  #30  
Old 03-16-2017, 09:46 PM
Melbourne Melbourne is offline
Guest
 
Join Date: Nov 2009
Posts: 3,189
Quote:
Originally Posted by Crafter_Man View Post
Excellent find, thank you! So I take back what I said. Well, sort of... I am still pretty sure you can't get a sustained arc at 12 V to 14 V. But you can certainly get an intermittent/sputtering arc at those voltage levels which will produce damage.

(As a side note, virtually all my experience in arc-related failures is for systems operating at 115 V / 400 Hz or 270 VDC. The latter in particular can produce some very impressive arcs. And sustainable ones at that. I don't have any experience w/ automotive arcs.)


At lower voltages you require a higher current to sustain an arc in air. When you are doing arc welding, if your electrode gets too close to the material, your arc will go out when your power supply doesn't supply the increased current required.. This will indead give you a sputtering arc: the power in the arc is the arc voltage times the arc current.

If you have enough current, it is indeed possible to weld at 6V. Aother problem then is, if the arc is short, it doesn't spread very much, and you weld a narrow hot spot, which is not what you want.
  #31  
Old 03-17-2017, 04:08 AM
Princhester Princhester is offline
Charter Member
 
Join Date: Jan 2001
Location: Brisbane, Australia
Posts: 14,257
Quote:
Originally Posted by Crafter_Man View Post
Excellent find, thank you!
Well it helps when you know and have worked with Peter on numerous occasions.

Last edited by Princhester; 03-17-2017 at 04:08 AM.
  #32  
Old 03-17-2017, 05:27 AM
bob++ bob++ is offline
Guest
 
Join Date: Jan 2013
Location: Worcestershire UK
Posts: 5,393
Interesting to read about the causes of fires in US Trucks. When I was involved in British haulage, I remember seeing a similar report about European trucks. In our case, electrical failures were at the bottom of the list; the most common cause being overheated tyres. This was most commonly due to underinflation or binding brakes. The second most likely cause was a mechanical failure in the engine; usually related to turbochargers.

Electrical fires, where they did occur were frequently due to the drivers overloading the in-cab circuits with their own equipment. It seems that otherwise sensible people will, when faced with a fuse that keeps blowing, put a higher rated one in, or even use aluminium foil.
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 06:41 AM.

Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

Send questions for Cecil Adams to: cecil@chicagoreader.com

Send comments about this website to: webmaster@straightdope.com

Terms of Use / Privacy Policy

Advertise on the Straight Dope!
(Your direct line to thousands of the smartest, hippest people on the planet, plus a few total dipsticks.)

Publishers - interested in subscribing to the Straight Dope?
Write to: sdsubscriptions@chicagoreader.com.

Copyright 2017 Sun-Times Media, LLC.

 
Copyright © 2017