> [@danceswithcats](#):
>
> In addition to your above notation, those receptacles downstream must also be marked “GFCI Protected” per 406.3 (D)(3)(c) 2005 NEC. Darn few folks comply with these requirements anyway. 😉

Yeah, I guess they think those stickers are in there to play with. Heh.

---

<div class="post-metadata">

**Author:** ![danceswithcats](https://avatars.discourse-cdn.com/v4/letter/d/9e8a1a/32.png) [@danceswithcats](https://boards.straightdope.com/u/danceswithcats)\
**Post date:** [March 19, 2006, 4:54am UTC](https://boards.straightdope.com/t/another-gfci-problem/348639/22 "2006-03-19T04:54:25Z")

</div>

> [@Q.E.D.](#):
>
> Yeah, I guess they think those stickers are in there to play with. Heh.

Customers with wallpapered receptacle covers don’t take kindly to those labels, either. Sorry, Ma’am-it has to go there. I know it looks icky.