# Electric motor doesn't start - likely problems?

**URL:** <https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482>\
**Category:** Factual Questions\
**Created:** [July 18, 2009, 10:34pm UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482 "2009-07-18T22:34:57Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![Running\_with\_Scissors](https://avatars.discourse-cdn.com/v4/letter/r/a183cd/32.png) [@Running\_with\_Scissors](https://boards.straightdope.com/u/Running_with_Scissors)\
**Post date:** [July 18, 2009, 10:34pm UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/1 "2009-07-18T22:34:57Z")

</div>

My central A/C air handler stopped working. The fan motor is a 220V single phase, capacitor start. The motor gets hot, the capacitor stays cool. The fan turns freely when pushed by hand, but pushing it does not get the motor running.

What are the most likely problems?

Thanks!

---

<div class="post-metadata">

**Author:** ![HongKongFooey](https://avatars.discourse-cdn.com/v4/letter/h/c4cdca/32.png) [@HongKongFooey](https://boards.straightdope.com/u/HongKongFooey)\
**Post date:** [July 19, 2009, 12:07am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/2 "2009-07-19T00:07:01Z")

</div>

It sounds like the start winding is opened but I think you should be able to get it to start by spinning the rotor (with power applied of course) if that were the case. I work on DC and three-phase motors so I’m a bit out of my element with single-phase but there used to be centrifugal switches to disconnect the start winding once the motor is at speed. Those can fail and keep the start winding in too long and burn the winding or the capacitor.

Can you give more info from the nameplate? Manufacturer, etc. It ould be nice to know whether the capacitor stays in the circuit or is disconnected on this one in normal operation. Also there may be a thermal overload that has tripped or failed.

---

<div class="post-metadata">

**Author:** ![Magiver](https://avatars.discourse-cdn.com/v4/letter/m/4491bb/32.png) [@Magiver](https://boards.straightdope.com/u/Magiver)\
**Post date:** [July 19, 2009, 12:27am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/3 "2009-07-19T00:27:43Z")

</div>

Your A/C “handler”. Do you mean the compressor cooling fan or the blower that moves the air in the house? The compressor cooling fan isn’t usually connected directly to the compressor. If the compressor isn’t turning then I would start with the relay that turns it on.

---

<div class="post-metadata">

**Author:** ![Snnipe\_70E](https://avatars.discourse-cdn.com/v4/letter/s/b5a626/32.png) [@Snnipe\_70E](https://boards.straightdope.com/u/Snnipe_70E)\
**Post date:** [July 19, 2009, 12:33am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/4 "2009-07-19T00:33:17Z")

</div>

> [@Running\_with\_Scissors](#):
>
> My central A/C air handler stopped working. The fan motor is a 220V single phase, capacitor start. The motor gets hot, the capacitor stays cool. The fan turns freely when pushed by hand, but pushing it does not get the motor running.
> 
> What are the most likely problems?
> 
> Thanks!

I assume you are talking about the condencer fan motor. If you can spin it by hand and it does not keep turnning there is a good chance that the motor has a major issue.

You need to call a pro.

---

<div class="post-metadata">

**Author:** ![Magiver](https://avatars.discourse-cdn.com/v4/letter/m/4491bb/32.png) [@Magiver](https://boards.straightdope.com/u/Magiver)\
**Post date:** [July 19, 2009, 1:15am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/5 "2009-07-19T01:15:58Z")

</div>

> [@Snnipe\_70E](#):
>
> I assume you are talking about the condencer fan motor. If you can spin it by hand and it does not keep turnning there is a good chance that the motor has a major issue.
> 
> You need to call a pro.

I’m not a HVAC person but I just gutted a bunch of A/C units for scrap and the cooling fans were 110 volt.

---

<div class="post-metadata">

**Author:** ![Snnipe\_70E](https://avatars.discourse-cdn.com/v4/letter/s/b5a626/32.png) [@Snnipe\_70E](https://boards.straightdope.com/u/Snnipe_70E)\
**Post date:** [July 19, 2009, 1:26am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/6 "2009-07-19T01:26:20Z")

</div>

> [@Magiver](#):
>
> I’m not a HVAC person but I just gutted a bunch of A/C units for scrap and the cooling fans were 110 volt.

Most cooling fans are 110. But condencer fans quite often ater 220.

---

<div class="post-metadata">

**Author:** ![Gbro](https://avatars.discourse-cdn.com/v4/letter/g/c6cbf5/32.png) [@Gbro](https://boards.straightdope.com/u/Gbro)\
**Post date:** [July 19, 2009, 1:41am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/7 "2009-07-19T01:41:37Z")

</div>

> [@Running\_with\_Scissors](#):
>
> My central A/C air handler stopped working. **The fan motor is a 220V single phase** , capacitor start. The motor gets hot, the capacitor stays cool. The fan turns freely when pushed by hand, but pushing it does not get the motor running.
> 
> What are the most likely problems?
> 
> Thanks!

If it is 220 V it is 2 phase. I would check all breakers or fuses. and then call a Pro like already advised if it is anything more than that.

---

<div class="post-metadata">

**Author:** ![raindog](https://avatars.discourse-cdn.com/v4/letter/r/2bfe46/32.png) [@raindog](https://boards.straightdope.com/u/raindog)\
**Post date:** [July 19, 2009, 4:03am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/8 "2009-07-19T04:03:39Z")

</div>

> [@Running\_with\_Scissors](#):
>
> My central A/C air handler stopped working. The fan motor is a 220V single phase, capacitor start. The motor gets hot, the capacitor stays cool. The fan turns freely when pushed by hand, but pushing it does not get the motor running.
> 
> What are the most likely problems?
> 
> Thanks!

You didn’t say whether the compressor runs. Does it? Because that takes us in another diagnostic direction.

If the compressor will run it indicates that the fuses are good and there is 220V present. (Do NOT let the compressor run for any length of time without the condensing fan motor)

If neither the compressor or the fan on top are running check the fuses first to make sure that 220V is present. You’ll need a meter for that.

If the breakers and fuses are good (the fuses will be in the disconnect box outside next to the unit) than I’d be looking at the capacitor.

You see, fans go bad. Compressors go bad. But they _rarely_ go bad together. If neither is running you likely have a voltage problem or a bad capacitor. Here is a picture of a “dual” capacitor:  
[http://www.mobilehomerepair.com/media/img/coleman/1498-5301.jpg](http://www.mobilehomerepair.com/media/img/coleman/1498-5301.jpg)

Notice that top of the capacitor is slightly recessed and absolutely flat. Look at your cap. If it is “swollen” on top or bulging it is a certainty that the cap is bad----and the likely source of the problem.

If it’s bad, don’t try to replace it without getting direction from us.

One last thing. Even if the compressor will run, you may still have a bad cap. On dual caps, sometimes only one side of the cap goes bad-----letting the compressor run but not the fan. It’s low hanging fruit, but it’s really common low hanging fruit: visually inspect the cap.

---

<div class="post-metadata">

**Author:** ![raindog](https://avatars.discourse-cdn.com/v4/letter/r/2bfe46/32.png) [@raindog](https://boards.straightdope.com/u/raindog)\
**Post date:** [July 19, 2009, 4:05am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/9 "2009-07-19T04:05:36Z")

</div>

> [@Magiver](#):
>
> I’m not a HVAC person but I just gutted a bunch of A/C units for scrap and the cooling fans were 110 volt.

They appear to be, but they are always 220V. (in the US anyway)

That said, someone is bound to post a hyperlink with a 110V condensing fan. But in 20 years I can’t remember seeing one _and I see thousands of them._

---

<div class="post-metadata">

**Author:** ![raindog](https://avatars.discourse-cdn.com/v4/letter/r/2bfe46/32.png) [@raindog](https://boards.straightdope.com/u/raindog)\
**Post date:** [July 19, 2009, 4:09am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/10 "2009-07-19T04:09:51Z")

</div>

> [@Magiver](#):
>
> Your A/C “handler”. Do you mean the compressor cooling fan or the blower that moves the air in the house? The compressor cooling fan isn’t usually connected directly to the compressor. If the compressor isn’t turning then I would start with the relay that turns it on.

If neither the fan or compressor run, it is possible that the ‘relay’ is bad. (although in these applications they use a definite purpose contactor)

Both the compressor and fan will route through the \*\*same \*\*contactor. We see bad contactors often enough to keep them on our trucks, but a more common cause is blown fuses (not to be confused with the fuses or breakers in the main electrical panel) or bad capacitors.

Contactors are pretty reliable devices.

---

<div class="post-metadata">

**Author:** ![raindog](https://avatars.discourse-cdn.com/v4/letter/r/2bfe46/32.png) [@raindog](https://boards.straightdope.com/u/raindog)\
**Post date:** [July 19, 2009, 4:13am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/11 "2009-07-19T04:13:44Z")

</div>

My guess with the very little information we’ve been given: a bad cap.

---

<div class="post-metadata">

**Author:** ![Magiver](https://avatars.discourse-cdn.com/v4/letter/m/4491bb/32.png) [@Magiver](https://boards.straightdope.com/u/Magiver)\
**Post date:** [July 19, 2009, 4:34am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/12 "2009-07-19T04:34:01Z")

</div>

By contactor do you mean relay? Mine sticks about once every 2 years.

---

<div class="post-metadata">

**Author:** ![raindog](https://avatars.discourse-cdn.com/v4/letter/r/2bfe46/32.png) [@raindog](https://boards.straightdope.com/u/raindog)\
**Post date:** [July 19, 2009, 4:38am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/13 "2009-07-19T04:38:39Z")

</div>

> [@Magiver](#):
>
> By contactor do you mean relay? Mine sticks about once every 2 years.

If it’s the contactor in the outdoor unit, and it looks anything like this: [http://www.supplierlist.com/photo\_images/12196/HLC-2X\_Series\_Definite\_Purpose\_Contactors\_.jpg](http://www.supplierlist.com/photo_images/12196/HLC-2X_Series_Definite_Purpose_Contactors_.jpg) than it acts like a relay, but it is called a contactor.

If yours is sticking it needs to be replaced. The contacts have been burned enough through repeated use that they are “fusing” together under load.

This can cause more damage down the road. When we see the contacts charred/burnt we replace the contactor as a preventive measure.

ETA: As a point of reference, we probably change 25 capacitors for every contactor we change. (give or take: I’m not certain of the exact ratio)

---

<div class="post-metadata">

**Author:** ![Snnipe\_70E](https://avatars.discourse-cdn.com/v4/letter/s/b5a626/32.png) [@Snnipe\_70E](https://boards.straightdope.com/u/Snnipe_70E)\
**Post date:** [July 19, 2009, 5:27am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/14 "2009-07-19T05:27:04Z")

</div>

> [@Gbro](#):
>
> If it is 220 V it is 2 phase. I would check all breakers or fuses. and then call a Pro like already advised if it is anything more than that.

NO there are very few 2 phase motors out there. 2 Phase power is a very strange and rare thing.

---

<div class="post-metadata">

**Author:** ![Magiver](https://avatars.discourse-cdn.com/v4/letter/m/4491bb/32.png) [@Magiver](https://boards.straightdope.com/u/Magiver)\
**Post date:** [July 19, 2009, 5:28am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/15 "2009-07-19T05:28:08Z")

</div>

> [@raindog](#):
>
> If it’s the contactor in the outdoor unit, and it looks anything like this: [http://www.supplierlist.com/photo\_images/12196/HLC-2X\_Series\_Definite\_Purpose\_Contactors\_.jpg](http://www.supplierlist.com/photo_images/12196/HLC-2X_Series_Definite_Purpose_Contactors_.jpg) than it acts like a relay, but it is called a contactor.
> 
> If yours is sticking it needs to be replaced. The contacts have been burned enough through repeated use that they are “fusing” together under load.
> 
> This can cause more damage down the road. When we see the contacts charred/burnt we replace the contactor as a preventive measure.
> 
> ETA: As a point of reference, we probably change 25 capacitors for every contactor we change. (give or take: I’m not certain of the exact ratio)

I think mine sticks because of corrosion but I’ll get my HVAC buddy to swap it out. the Ford museum might be interested in it.

---

<div class="post-metadata">

**Author:** ![Magiver](https://avatars.discourse-cdn.com/v4/letter/m/4491bb/32.png) [@Magiver](https://boards.straightdope.com/u/Magiver)\
**Post date:** [July 19, 2009, 5:59am UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/16 "2009-07-19T05:59:16Z")

</div>

If it’s the contactor than wacking it with a piece of wood may bring it back online and that would be a clear indication of what to replace. If nothing else, it will allow some frustration to be vented.

---

<div class="post-metadata">

**Author:** ![Running\_with\_Scissors](https://avatars.discourse-cdn.com/v4/letter/r/a183cd/32.png) [@Running\_with\_Scissors](https://boards.straightdope.com/u/Running_with_Scissors)\
**Post date:** [July 19, 2009, 2:00pm UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/17 "2009-07-19T14:00:01Z")

</div>

The air handler is the inside unit; i.e., the evaporator. This is the fan that circulates air through the house. It is definitely 220volt, 1 phase. And while I haven’t checked for power, the fact that the motor is getting hot is a pretty good indication that it’s getting it (also, I could hear a hum coming from the motor until I shut the breaker off).

Here’s the info from the plate:

Emerson K55HXEKD-7575  
208-230 Volts  
825 RPM  
3 speed  
PT #34K7601  
1/3 HP

Note that while it is a 3 speed motor, only the common and high speed terminals are connected (plus the capacitor, of course).

---

<div class="post-metadata">

**Author:** ![raindog](https://avatars.discourse-cdn.com/v4/letter/r/2bfe46/32.png) [@raindog](https://boards.straightdope.com/u/raindog)\
**Post date:** [July 19, 2009, 2:40pm UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/18 "2009-07-19T14:40:22Z")

</div>

> [@Running\_with\_Scissors](#):
>
> The air handler is the inside unit; i.e., the evaporator. This is the fan that circulates air through the house. It is definitely 220volt, 1 phase. And while I haven’t checked for power, the fact that the motor is getting hot is a pretty good indication that it’s getting it (also, I could hear a hum coming from the motor until I shut the breaker off).
> 
> Here’s the info from the plate:
> 
> Emerson K55HXEKD-7575  
> 208-230 Volts  
> 825 RPM  
> 3 speed  
> PT #34K7601  
> 1/3 HP
> 
> Note that while it is a 3 speed motor, only the common and high speed terminals are connected (plus the capacitor, of course).

If it is the indoor fan than there are 2 likely causes, in order of likeliness:

**1) A bad cap.** If the motor is hot (and the wheel will spin freely by hand, indication that it’s not bound up) than it is likely that 220V is being applied. If it is the capacitor on the indoor blower, it will not bulge----but can be bad all the same.

**2) A bad motor** Sometimes bad things happen to good motors. 😉

The fact that the motor is hot suggests that the windings are not open, and that the cap is the problem.

If you want to try this and avoid a tech visit, replace the cap. The other thing you can try (with the power off, of course) is to switch the motor leads. Take one of the leads not being used and put it where the one that is being used is; IOW, switch fan speeds.

---

<div class="post-metadata">

**Author:** ![Running\_with\_Scissors](https://avatars.discourse-cdn.com/v4/letter/r/a183cd/32.png) [@Running\_with\_Scissors](https://boards.straightdope.com/u/Running_with_Scissors)\
**Post date:** [July 19, 2009, 4:40pm UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/19 "2009-07-19T16:40:14Z")

</div>

Awesome response, thanks. I will try switching the leads. If not, where do I find a replacement capacitor? I assume it’s not the sort of thing Lowes would carry. Would an electrical supply store have it, or would I have to seek out a place that specializes in motors?

---

<div class="post-metadata">

**Author:** ![raindog](https://avatars.discourse-cdn.com/v4/letter/r/2bfe46/32.png) [@raindog](https://boards.straightdope.com/u/raindog)\
**Post date:** [July 19, 2009, 5:05pm UTC](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482/20 "2009-07-19T17:05:50Z")

</div>

A small motor repair shop, or an HVAC or appliance repair wholesaler mostly.

The old cap will have 2 pieces of info, as an example, 10uf @370 VAC or something like that. Your unit will likely have a 7.5, 10 or 15 uf (some have 12.5) and either 370 VAC or 440 VAC.

You can use a larger voltage rating—like use a 440 VAC instead of a 370 VAC; you just shouldn’t use a smaller one, a 370 VAC instead of a 440 VAC.

[Next page](https://boards.straightdope.com/t/electric-motor-doesnt-start-likely-problems/503482.md?page=2)