Here’s what I found out, and why:
The guy at the home improvement store said that you can you an extension cord with a space heater, but it can only be a maximum of 6 feet . . . use the grey one, for appliances (14 AWG, 1875W).
I saw in the FAQ for another space heater, that this is what you’d want to do, also, if you have to use an extension cord.
But, from talking to customer support of my space heater, I will not be using an extension cord. Why?
Do not use an extension cord with the space heater, because:
1.) They can’t handle the amperage and wattage
2.) The circuit breaker might not pop, because there’s a longer travel distance, and the feedback would be less direct to the thermal and magnetic mechanisms in the circuit breaker . . . An extension cord lowers the chance that the circuit breaker will be able to sense increasing heat from the wire . . . When you introduce an extension cord into the circuit, experience has shown that things can go on that you’re not going to know about [it would be good to have more specific info here]
Q: The 6’, 14 AWG, 1875W grey appliance extension cord says that it’s for use with appliances like air conditioners. So, why not with a space heater?
A: Space heaters are constantly drawing the amps, and do not peak down, as you see with air conditioners or refrigerators . . . It seems like there should be a spec for the cord as to how long it can handle high amps: sporadically vs. infrequently . . . I don’t think that this is common knowledge
How long can a 14 AWG wire handle 12.5 amps / 1500 W? Some have found that the extension cord will get warm. That’s not good.
Do not use the space heater in a bathroom, because:
1.) There is dust in the air, it gets damp, and the dust particles will accumulate on parts inside of the space heater
2.) Moisture is in the air. Moisture will stay in the space heater - it is not evaporated. Moisture and electronics do not mix well.
3.) The space heater will become a fire hazard
http://www.nashobapublishing.com/ci_27281615/fire-marshal-issues-cold-weather-fire-safety-warning
Space heaters need space, so use them in a 3-foot circle of safety, free of anything that can catch fire.
He added, “Space heaters are not designed to replace your central heating system, they are only designed to provide a little extra heat on a temporary basis.
So be sure to turn them off when you leave room or go to bed at night.” [that’s when I want to use it at 66F, from 10 pm to 6 am, when my gas furnace is set to 61F (68F in the daytime)]
It is best to plug space heaters and other heat-generating appliances directly into the outlet.
Overloaded extension cords cause many space heater fires. If you must use an extension cord, make sure it is rated for the same wattage as the appliance and use only one. [this is bad information]
goodsonengineering.com/wp-content/uploads/2011/08/CircuitBreakerMyths_web.pdf
basic breaker operation and design
In order to debunk the myths it is important to understand the basic operation and design of the trip mechanisms in a circuit breaker.
The thermal portion of the circuit breaker works by use of a bi-metallic strip which causes a spring-loaded latch to release and trip the breaker.
The deflection of the bi-metallic strip depends on the temperature, thus the breaker has a trip temperature and it is the heat generated within the breaker that causes the temperature to rise, the faster
the heat rise, the faster the breaker reaches temperature and trips.
Heat is directly proportional to the power (watts), which is proportional to the square of the current (P=I2 x R)
For example, if we assume that an extension cord is rated at 10 amperes (#18 AWG) and is carrying a load of 25 amperes while connected to a branch circuit wire that is protected by a 20 ampere T-M breaker, the 20 ampere breaker may never trip.
Relocatable power taps, more often called power strips, all have circuit breakers present.
In general, these breakers are thermal breakers, and have no magnetic trip level.
They are intended to prevent damage to wiring caused by having too many appliances plugged in (i.e., too great a load), and are usually rated at 15 amperes.
We mention these breakers because they are common, and yet they are very different from the T-M breaker used as a part of branch circuit wiring.
[Do they have a power strip with magnetic trip, or a portable plug-in circuit breaker? Looks like they do for contractors, but maybe it wouldn’t play well with the circuit breaker, like how if you put a GFCI downline from another GFCI, which are both downline from the circuit breaker, which is something you might do, if you don’t understand how these things are designed to work, ie. you shouldn’t put a GFCI downline from another GFCI.]
01/09/15 … Instead of putting the space heater on an extension cord, I’m going to go the other way, and get the computer equipment on a different branch circuit, with two 25 foot, 14 AWG extension cords (14 AWG is good for 15 amps, up to 25 feet) . . . Current thinking: Use some wire ties to hold them together, and duct tape to hold them down on the carpet, especially under the door. Make sure that the door doesn’t abrade the insulation of the extension cords. Be extra aware to not trip over them.
. . . . . could I have done this with just one extension cord, and a built-in splitter on the end? . . . because one extension cord can handle 15 amps . . . maybe, but it can’t hurt to split them for an extra $20 (the extension cords were $19.97 each) . . . maybe things will run cooler
keywords for further research: extension cord for space heater, fire marshal