# Electrical wiring help please - GFCI wiring related

**URL:** <https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749>\
**Category:** Factual Questions\
**Tags:** tools-electric-diy\
**Created:** [April 16, 2023, 5:04pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749 "2023-04-16T17:04:26Z")\
**Posts on this page:** 20\
**Page:** 2

<div class="post-metadata">

**Author:** ![Crafter\_Man](https://sea3.discourse-cdn.com/straightdope/user_avatar/boards.straightdope.com/crafter_man/32/458_2.png) [@Crafter\_Man](https://boards.straightdope.com/u/Crafter_Man)\
**Post date:** [April 17, 2023, 1:24am UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/21 "2023-04-17T01:24:00Z")

</div>

> [@DavidNRockies](#):
>
> If I’m seeing things correctly in the pics, isn’t that a metal two-gang box, and shouldn’t IT be grounded anyway

The OP said there was no ground wire.

Yea, the metal box _might_ be grounded via conduit connections back to the breaker box. It’s something that can be measured.

---

<div class="post-metadata">

**Author:** ![Crafter\_Man](https://sea3.discourse-cdn.com/straightdope/user_avatar/boards.straightdope.com/crafter_man/32/458_2.png) [@Crafter\_Man](https://boards.straightdope.com/u/Crafter_Man)\
**Post date:** [April 17, 2023, 1:27am UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/22 "2023-04-17T01:27:54Z")

</div>

> [@Mean\_Mr.Mustard](#):
>
> Knowing this, can we conclude that the red wire is hot (and should be connected to LINE on the GFCI and not LOAD)?

Yes, it is probably hot. But given the fact that there’s some sketchy things previously homeowners did (stranded wire, wrapping wire under screwhead in CCW direction), I would want to be 100% sure. See my previous posts. Just run a long extension cord to a grounded outlet, and make voltage measurements vs. ground.

You… did place an order for a digital DMM from Amazon, yes? [Here](https://www.amazon.com/AstroAI-Digital-Multimeter-Voltage-Tester/dp/B01ISAMUA6/) is one for $10.

---

<div class="post-metadata">

**Author:** ![markn\_1](https://avatars.discourse-cdn.com/v4/letter/m/f9ae1b/32.png) [@markn\_1](https://boards.straightdope.com/u/markn_1)\
**Post date:** [April 17, 2023, 2:30am UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/23 "2023-04-17T02:30:26Z")

</div>

In the house I grew up in, built in 1912 and probably having its wiring modified multiple times by various people of various qualifications over the years, all the wall switches switched the neutral wire rather than the hot wire. They worked, but of course were not wired “correctly” (nor safely). So I wouldn’t assume a wire is hot just because it is switched.

The switches in my house were also oriented so they were “on” when the switch was down and “off” when the switch was up. Those wacky guys.

---

<div class="post-metadata">

**Author:** ![Snipe70e](https://avatars.discourse-cdn.com/v4/letter/s/51bf81/32.png) [@Snipe70e](https://boards.straightdope.com/u/Snipe70e)\
**Post date:** [April 17, 2023, 4:46am UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/24 "2023-04-17T04:46:04Z")

</div>

> [@Crafter\_Man](#):
>
> Just run a long extension cord to a grounded outlet, and make voltage measurements vs. ground.

That might be easier said than done. If the out let is 2 prong without a ground and there is no ground wire there is a good chance this is an older house with only 2 wire and no grounds.

But you can try checking all wires to the conduit. If and I say If you get 120 volts from a wire to the conduit then the house was using the conduit as a ground.

---

<div class="post-metadata">

**Author:** ![Mean\_Mr.Mustard](https://sea3.discourse-cdn.com/straightdope/user_avatar/boards.straightdope.com/mean_mr.mustard/32/3865_2.png) [@Mean\_Mr.Mustard](https://boards.straightdope.com/u/Mean_Mr.Mustard)\
**Post date:** [April 17, 2023, 11:07am UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/25 "2023-04-17T11:07:40Z")

</div>

> [@Crafter\_Man](#):
>
> …wrapping wire under screwhead in CCW direction

Wow, I did not even catch that!

> [@Crafter\_Man](#):
>
> You… did place an order for a digital DMM from Amazon, yes? [Here](https://www.amazon.com/AstroAI-Digital-Multimeter-Voltage-Tester/dp/B01ISAMUA6/) is one for $10.

Well, it is in my “save for later” folder. Does that count?

mmm

---

<div class="post-metadata">

**Author:** ![DavidNRockies](https://sea3.discourse-cdn.com/straightdope/user_avatar/boards.straightdope.com/davidnrockies/32/6279_2.png) [@DavidNRockies](https://boards.straightdope.com/u/DavidNRockies)\
**Post date:** [April 17, 2023, 11:53am UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/26 "2023-04-17T11:53:30Z")

</div>

> [@Snipe70e](#):
>
> That might be easier said than done. If the out let is 2 prong without a ground and there is no ground wire there is a good chance this is an older house with only 2 wire and no grounds.

That’s the impression I’m getting, too. Grounding became code in 1962.

**mmm** : the GFCI _is_ the one code-compliant workaround in this situation, but … just an FYI … you may want to consider the situation, writ large, at some point:

> **[Buying a House With Ungrounded Outlets? Here's What You Should Know](https://www.newwestern.com/blog/buying-a-house-with-ungrounded-outlets-heres-what-you-should-know/)**
>
> Should you buy a house with ungrounded outlets? We cover that question and more. Read on to learn more!

> **[How to Convert an Electrical Outlet From Non-Grounded to Grounded | Hunker](https://www.hunker.com/13414308/how-to-convert-an-electrical-outlet-from-non-grounded-to-grounded)**
>
> The easiest way to change an ungrounded outlet to a grounded one is to replace it with a ground fault interrupting outlet (GFI).

> <https://diy.stackexchange.com/questions/267563/grounding-receptacles-with-metal-boxes-still-showing-open-ground>

---

<div class="post-metadata">

**Author:** ![engineer\_comp\_geek](https://sea3.discourse-cdn.com/straightdope/user_avatar/boards.straightdope.com/engineer_comp_geek/32/504_2.png) [@engineer\_comp\_geek](https://boards.straightdope.com/u/engineer_comp_geek)\
**Post date:** [April 17, 2023, 12:16pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/27 "2023-04-17T12:16:02Z")

</div>

Having both red and black wires makes me think that there is a 3 way switch involved here.

But then the use of stranded wire plus the counter-clockwise wire under the screwhead makes it pretty clear that whoever wired this had no idea what they were doing, so all bets are off.

While I am generally all for people figuring out how to do things on their own, given the OP’s lack of test equipment and lack of experience I think calling in a skilled electrician is the best option at this point.

Normally you can assume that things were done mostly to code and can figure out from looking at it what goes where. But in this case, you need to assume that whoever did the wiring was a complete idiot and could have done almost anything. That makes troubleshooting a lot more difficult. At a bare minimum I would say the OP needs to buy a multimeter, and if the paths of the conduits aren’t obvious, I would also buy one of those wire tracers that sends RF down the line and then uses a handheld receiver to follow along the wire and trace where it actually goes.

---

<div class="post-metadata">

**Author:** ![DavidNRockies](https://sea3.discourse-cdn.com/straightdope/user_avatar/boards.straightdope.com/davidnrockies/32/6279_2.png) [@DavidNRockies](https://boards.straightdope.com/u/DavidNRockies)\
**Post date:** [April 17, 2023, 12:28pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/28 "2023-04-17T12:28:16Z")

</div>

It’d be really hard to argue with **E\_C\_G** on this one.

Further, how old IS the house? Pre-1962 almost surely means an ungrounded panel. Pre-1950 might take us into **[knob and tube](https://inspectapedia.com/electric/Knob_and_Tube_Wiring.php)** territory – yet another wrench in the works.

Also note this quote from the link above:

> (A homeowner cannot safely test a GFCI while it is in place, installed on an electrical circuit that has no ground but the GFCI can still be expected to work correctly if it is wired properly.)

Not being able to check my own work in this situation, IMHO, is a pretty big cause for pause.

---

<div class="post-metadata">

**Author:** ![DavidNRockies](https://sea3.discourse-cdn.com/straightdope/user_avatar/boards.straightdope.com/davidnrockies/32/6279_2.png) [@DavidNRockies](https://boards.straightdope.com/u/DavidNRockies)\
**Post date:** [April 17, 2023, 12:40pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/29 "2023-04-17T12:40:17Z")

</div>

One other ?, **mmm** : My eyes aren’t so good, but are you in Cali and is that redwood framing?

That would spell “pretty damned old” to me. Our last San Diego house had a redwood framed detached garage and that house was from about 1916.

---

<div class="post-metadata">

**Author:** ![Mean\_Mr.Mustard](https://sea3.discourse-cdn.com/straightdope/user_avatar/boards.straightdope.com/mean_mr.mustard/32/3865_2.png) [@Mean\_Mr.Mustard](https://boards.straightdope.com/u/Mean_Mr.Mustard)\
**Post date:** [April 17, 2023, 12:54pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/30 "2023-04-17T12:54:26Z")

</div>

Random answers:

First of all, I really appreciate all the input.  
The house is a bungalow, built in 1950. No knob and tube.  
Not in California, no redwood.  
No 3-way switch.  
The fact that the installer made some obvious blunders, as some of you have pointed out, makes me not want to mess with it further. I am going to leave this one to a pro.  
And I will make a point to be there with them while they resolve this. There is much more I can learn here.  
Finally, yeah, I am going to buy a mutlimeter, just because I should have one. 🙂

mmm

---

<div class="post-metadata">

**Author:** ![Crafter\_Man](https://sea3.discourse-cdn.com/straightdope/user_avatar/boards.straightdope.com/crafter_man/32/458_2.png) [@Crafter\_Man](https://boards.straightdope.com/u/Crafter_Man)\
**Post date:** [April 17, 2023, 12:55pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/31 "2023-04-17T12:55:46Z")

</div>

> A homeowner cannot safely test a GFCI while it is in place, installed on an electrical circuit that has no ground…

If a GFCI receptacle is not grounded, its ground-fault circuitry cannot be tested using an [external tester](https://www.homedepot.com/p/Klein-Tools-GFCI-Tester-RT210/206517824). But the test/reset buttons on the receptacle itself will still work.

---

<div class="post-metadata">

**Author:** ![Uncommon\_Sense](https://avatars.discourse-cdn.com/v4/letter/u/f9ae1b/32.png) [@Uncommon\_Sense](https://boards.straightdope.com/u/Uncommon_Sense)\
**Post date:** [April 17, 2023, 1:57pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/32 "2023-04-17T13:57:38Z")

</div>

Good info in this thread, but very confusing for a beginner.  
I’ve been a sparky for 35 years.

From what I can tell, the switch is on the load side of the circuit. Someone tapped the circuit in the box, added a switch and extended the wires to a light or something.

The easiest way to see if the box is grounded is to take a resistance reading from the white neutral wires (either, try one at a time) to the device box. If you get 0 ohms on either one, then you have a grounded box. This is because the neutral and the metal raceways are bonded in the electrical panel. If you don’t have a ground, you can still install a GFCI - in fact, it’s recommended on ungrounded circuits, you just have to label it as such.

Firstly, I would have simply installed a GFCI breaker (replace the one that feeds the garage) in the main panel instead of trying to rewire the garage. This should be done by a sparky though.

Lastly, from what I’ve read, you have 4 wires to deal with. Without a meter I would make these assumptions based on experience - The new pair (red and white) and the older pair (black and black/white - we will assume original wiring and will come from the breaker). The red and white will be the load and the black and black/white will be the line wiring (as applied to the new GFCI). If you tried to wire the new GFCI this way and were not successful it may be that you didn’t reset the GFCI prior to testing, or your touchless voltage sensor is shot. It looks like you have a plug in tester as well, that should have worked fine.

I see that on one of your many trials you had a green light on the GFCI, that should have been the “correct” install. Make sure the reset button is pushed in and then hit the test button. You should hear it snap and the reset button will pop out. Reset again and then plug in your tester.

With a proper multimeter this job takes 30 seconds to figure out.  
Turn off power.  
Seperate all wires in box so they aren’t touching.  
Using the Multimeter, find the neutral that is bonded to the box (0-Ohms).  
(The other neutral wire should have infinite Ohms.)  
The wire that is in the same conduit as the neutral with 0-Ohms will be your hot from the breaker.  
The other two wires are your load.  
The above assumes you don’t have incorrectly wired outlets elswhere or two neutrals from separate circuits spliced together somewhere.  
What you are going through right now, is why electricians should be involved in any re-wiring efforts.

---

<div class="post-metadata">

**Author:** ![Uncommon\_Sense](https://avatars.discourse-cdn.com/v4/letter/u/f9ae1b/32.png) [@Uncommon\_Sense](https://boards.straightdope.com/u/Uncommon_Sense)\
**Post date:** [April 17, 2023, 2:00pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/33 "2023-04-17T14:00:40Z")

</div>

What city is this in?

---

<div class="post-metadata">

**Author:** ![Uncommon\_Sense](https://avatars.discourse-cdn.com/v4/letter/u/f9ae1b/32.png) [@Uncommon\_Sense](https://boards.straightdope.com/u/Uncommon_Sense)\
**Post date:** [April 17, 2023, 2:13pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/34 "2023-04-17T14:13:46Z")

</div>

> [@Mean\_Mr.Mustard](#):
>
> Yes, it is a metal box. I guess I just assumed it was not grounded because I didn’t see any obvious grounding wire. Maybe it is.
> 
> And yeah, it did occur to me that the GFCI may have been tripped. It was not.
> 
> mmm

When you checked you should have hit the test button and then the reset button to verify operation. If you got the reset button to pop then you have it wired correctly. You might have to hit the buttons in this order depending on make/model - reset/test/reset OR test/reset/test/reset. I like to cycle the test/reset a couple of times to make sure the thing works.  
It’s likely that you had this thing wired correctly once and didn’t know it.

---

<div class="post-metadata">

**Author:** ![Mean\_Mr.Mustard](https://sea3.discourse-cdn.com/straightdope/user_avatar/boards.straightdope.com/mean_mr.mustard/32/3865_2.png) [@Mean\_Mr.Mustard](https://boards.straightdope.com/u/Mean_Mr.Mustard)\
**Post date:** [April 17, 2023, 4:08pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/35 "2023-04-17T16:08:10Z")

</div>

> [@Uncommon\_Sense](#):
>
> It’s likely that you had this thing wired correctly once and didn’t know it.

I believe this is probably true.

> [@Uncommon\_Sense](#):
>
> The easiest way to see if the box is grounded is to take a resistance reading from the white neutral wires (either, try one at a time) to the device box. If you get 0 ohms on either one, then you have a grounded box.

In my case I have one white, one red, and two black. I am assuming that I would take a resistance reading from the white and again from the red?

> [@Uncommon\_Sense](#):
>
> Using the Multimeter, find the neutral that is bonded to the box (0-Ohms).  
> (The other neutral wire should have infinite Ohms.)  
> The wire that is in the same conduit as the neutral with 0-Ohms will be your hot from the breaker.

Would this only work if the box is grounded?  
Suppose I do not get 0 ohms on either the white or red wire, how should I proceed then?

mmm

---

<div class="post-metadata">

**Author:** ![Mean\_Mr.Mustard](https://sea3.discourse-cdn.com/straightdope/user_avatar/boards.straightdope.com/mean_mr.mustard/32/3865_2.png) [@Mean\_Mr.Mustard](https://boards.straightdope.com/u/Mean_Mr.Mustard)\
**Post date:** [April 17, 2023, 4:10pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/36 "2023-04-17T16:10:51Z")

</div>

@Uncommon_Sense, I would really like your input on this question:

> [@Mean\_Mr.Mustard](#):
>
> OK, back to basics…
> 
> (the following is with respect to the original outlet, before I even started monkeying around with it):
> 
> 1. The red wire runs from a brass screw to a switch.
> 2. With the switch on, the outlet has power
> 3. With the switch off, the outlet has no power
> 
> Knowing this, can we conclude that the red wire is hot (and should be connected to LINE on the GFCI and not LOAD)?
> 
> mmm

---

<div class="post-metadata">

**Author:** ![Uncommon\_Sense](https://avatars.discourse-cdn.com/v4/letter/u/f9ae1b/32.png) [@Uncommon\_Sense](https://boards.straightdope.com/u/Uncommon_Sense)\
**Post date:** [April 17, 2023, 4:29pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/37 "2023-04-17T16:29:51Z")

</div>

Probably, but I would still test this with the Meter to be certain that something goofy isn’t going on with the wiring (like the colors are all jangled up and the switch is actually switching the neutral or something). With out verifying what are actually the neutrals and/or the hots - we are speculating.

However, if we assume that the red is the (switched) hot, then yes you are correct. AND we also assume that the white is the real neutral then - the red would be the LINE hot wire and the white will be the LINE neutral. The black wires will likely be as follows: the one that was on the left side of the (old) 2 wire outlet will be the load line, and the one that was on the right would be the load neutral.  
To simplify, you have 4 wires on the GFCI, (2) neutrals (line and load) and (1) switched line and (1) load line.

---

<div class="post-metadata">

**Author:** ![FluffyBob](https://avatars.discourse-cdn.com/v4/letter/f/ecb155/32.png) [@FluffyBob](https://boards.straightdope.com/u/FluffyBob)\
**Post date:** [April 17, 2023, 11:45pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/38 "2023-04-17T23:45:57Z")

</div>

I know you are trying to figure this out on your own and you are almost there, but this is the sort of situation where it usually is cheaper in the long run to have just got an electrician in the first place. No I told you so, just communcating where Ive gotten with this sort of stuff.

I am no electrician, I’m a general contractor / carpenter. I had thought that conduits were grounded, but maybe not in old systems. That being said, it is relatively easy to upgrade an old outlet to grounded by adding a run of 14 gauge to the nearest pipe / buried chunk of metal. Usually ive left this up to the electri ian, but its a pretty simple procedure.

---

<div class="post-metadata">

**Author:** ![DavidNRockies](https://sea3.discourse-cdn.com/straightdope/user_avatar/boards.straightdope.com/davidnrockies/32/6279_2.png) [@DavidNRockies](https://boards.straightdope.com/u/DavidNRockies)\
**Post date:** [April 17, 2023, 11:57pm UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/39 "2023-04-17T23:57:04Z")

</div>

> [@FluffyBob](#):
>
> That being said, it is relatively easy to upgrade an old outlet to grounded by adding a run of 14 gauge to the nearest pipe / buried chunk of metal. Usually ive left this up to the electri ian, but its a pretty simple procedure.

There are really a good number of important caveats to that old-school approach:

> **[You can use water pipes for grounding purposes, but... | EEP](https://electrical-engineering-portal.com/water-pipes-grounding-purposes)**
>
> Water pipes have been used extensively in the past as a grounding electrode. Water pipe connections are not testable and are unreliable due to the use of

One thing to consider is the possibility that parts of the plumbing system either have been, or will be, repaired or replaced by plastics. Even just a fitting here or there could cause problems in certain circumstances.

---

<div class="post-metadata">

**Author:** ![Snipe70e](https://avatars.discourse-cdn.com/v4/letter/s/51bf81/32.png) [@Snipe70e](https://boards.straightdope.com/u/Snipe70e)\
**Post date:** [April 18, 2023, 4:43am UTC](https://boards.straightdope.com/t/electrical-wiring-help-please-gfci-wiring-related/982749/40 "2023-04-18T04:43:07Z")

</div>

> [@FluffyBob](#):
>
> I am no electrician, I’m a general contractor / carpenter. I had thought that conduits were grounded, but maybe not in old systems. That being said, it is relatively easy to upgrade an old outlet to grounded by adding a run of 14 gauge to the nearest pipe / buried chunk of metal. Usually ive left this up to the electri ian, but its a pretty simple procedure.

Conduit should be grounded because it should run from the electrical box to the main electrical panel box. But what can happen is a loose fitting or a fitting becomes corroded breaking that ground.

Depending on the condition of the conduit and how it was ran it may be possible to pull a new ground wire through the conduit back to the main panel. But it would be best to have an electrician check this out and pull the wire.

I may be wrong but by the picture that does not really look like conduit, but may be pipe.