Okay - I did a little research and found OSHA’s report on the collapse, here: https://www.osha.gov/doc/engineering/2008_12_19.html
It turns out that the structural design of the actual bridge was found to be ‘‘generally in compliance with industry standards’’. And while the expected deflections were greater than desirable, this was considered a potential serviceability concern as opposed to a safety issue.
The walkway collapsed during construction due to failure of the temporary shoring, which was a result of several things going wrong, including:
-
Under-design of the temp shoring beams.
-
Designing the the temp shoring beams for high-strength steel but not bothering to tell anyone in manufacturing/construction. (The temp shoring would still have been under-designed, but the use of regular strength steel made it that much worse.)
-
Using 3 beams that were delivered significantly smaller than called for in the temp shoring design - W10x12 instead of W10x19.
-
Not constructing the temp shoring according to design by increasing the distance between shoring towers, inadequate soil anchor embedment and lack of lateral bracing via diagonal cables between anchors.
In short, I didn’t find any mention that the minimal difference between the weight of wet conctrete and cured concrete contributed to the collapse in any way.