# Pressure rise in a fire sprinkler system?

**URL:** <https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332>\
**Category:** Factual Questions\
**Created:** [June 19, 2009, 8:47pm UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332 "2009-06-19T20:47:29Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![mangeorge](https://avatars.discourse-cdn.com/v4/letter/m/d78d45/32.png) [@mangeorge](https://boards.straightdope.com/u/mangeorge)\
**Post date:** [June 19, 2009, 8:47pm UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/1 "2009-06-19T20:47:29Z")

</div>

What could cause the pressure in a wet pipe fire sprinkler systen to rise from a normal of 75psi to 350psi? The pressure immediately drops back to normal when a drain valve is even slightly cracked.  
Trapped air, maybe?  
Peace,  
mangeorge

---

<div class="post-metadata">

**Author:** ![NinetyWt](https://avatars.discourse-cdn.com/v4/letter/n/cc9497/32.png) [@NinetyWt](https://boards.straightdope.com/u/NinetyWt)\
**Post date:** [June 19, 2009, 9:00pm UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/2 "2009-06-19T21:00:29Z")

</div>

Where are you measuring this (what part of the system)?

I suppose water hammer could cause this, briefly. If there aren’t any backflow valves on the thing.

---

<div class="post-metadata">

**Author:** ![mangeorge](https://avatars.discourse-cdn.com/v4/letter/m/d78d45/32.png) [@mangeorge](https://boards.straightdope.com/u/mangeorge)\
**Post date:** [June 19, 2009, 10:54pm UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/3 "2009-06-19T22:54:57Z")

</div>

> [@NinetyWt](#):
>
> Where are you measuring this (what part of the system)?
> 
> I suppose water hammer could cause this, briefly. If there aren’t any backflow valves on the thing.

There are a couple guages near the foam check valve, near the tank.  
There’s another guage at the valve where the system joins the utility water, and it indicates the same pressure. And the pressure staus high until we open the drain valve.

---

<div class="post-metadata">

**Author:** ![Moonshiner](https://avatars.discourse-cdn.com/v4/letter/m/9fc29f/32.png) [@Moonshiner](https://boards.straightdope.com/u/Moonshiner)\
**Post date:** [June 19, 2009, 11:08pm UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/4 "2009-06-19T23:08:56Z")

</div>

Municipal water? No pumps in the building involved?

---

<div class="post-metadata">

**Author:** ![sailor](https://avatars.discourse-cdn.com/v4/letter/s/a587f6/32.png) [@sailor](https://boards.straightdope.com/u/sailor)\
**Post date:** [June 19, 2009, 11:12pm UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/5 "2009-06-19T23:12:28Z")

</div>

> [@mangeorge](#):
>
> There are a couple guages near the foam check valve, near the tank.  
> There’s another guage at the valve where the system joins the utility water, and it indicates the same pressure. And the pressure staus high until we open the drain valve.

What’s a “guage”?

If you shut off the input to the system, say with a check valve, the water can expand and cause a huge rise in pressure which a small leak will promptly alleviate.

Any system which can be closed off like that should have a pressure relief valve. Like a water heater does.

---

<div class="post-metadata">

**Author:** ![mangeorge](https://avatars.discourse-cdn.com/v4/letter/m/d78d45/32.png) [@mangeorge](https://boards.straightdope.com/u/mangeorge)\
**Post date:** [June 19, 2009, 11:20pm UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/6 "2009-06-19T23:20:17Z")

</div>

> [@Moonshiner](#):
>
> Municipal water? No pumps in the building involved?

Yes, city water. It’s for a pilot plant inside a single story building. There are there wet glass bulb sprinklers, and when one of these releases it causes the foam to flow to two foam nozzles by activating the foam valve.

---

<div class="post-metadata">

**Author:** ![mangeorge](https://avatars.discourse-cdn.com/v4/letter/m/d78d45/32.png) [@mangeorge](https://boards.straightdope.com/u/mangeorge)\
**Post date:** [June 19, 2009, 11:23pm UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/7 "2009-06-19T23:23:55Z")

</div>

> [@sailor](#):
>
> What’s a “guage”?
> 
> If you shut off the input to the system, say with a check valve, the water can expand and cause a huge rise in pressure which a small leak will promptly alleviate.
> 
> Any system which can be closed off like that should have a pressure relief valve. Like a water heater does.

It’s a dyslexic gauge.  
Water expands at ambient (50 - 80 degrees F) temperatures?

---

<div class="post-metadata">

**Author:** ![sailor](https://avatars.discourse-cdn.com/v4/letter/s/a587f6/32.png) [@sailor](https://boards.straightdope.com/u/sailor)\
**Post date:** [June 19, 2009, 11:42pm UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/8 "2009-06-19T23:42:40Z")

</div>

> [@mangeorge](#):
>
> It’s a dyslexic gauge.  
> Water expands at ambient (50 - 80 degrees F) temperatures?

Are you serious? How do you think a thermometer works?

> [@](#):
>
> [Thermal expansion - Wikipedia](http://en.wikipedia.org/wiki/Coefficient_of_thermal_expansion)
> 
> coefficient of volumetric thermal expansion β in ppm/K at 20 °C
> 
> Water 207  
> Steel 36

---

<div class="post-metadata">

**Author:** ![HongKongFooey](https://avatars.discourse-cdn.com/v4/letter/h/c4cdca/32.png) [@HongKongFooey](https://boards.straightdope.com/u/HongKongFooey)\
**Post date:** [June 20, 2009, 12:39am UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/9 "2009-06-20T00:39:00Z")

</div>

We get this problem periodically on some of our systems in the summer months when it gets really hot inside.We had to switch to a different type sprinkler head because the pressure would get high enough to blow one off once in a while.

---

<div class="post-metadata">

**Author:** ![drachillix](https://avatars.discourse-cdn.com/v4/letter/d/48db29/32.png) [@drachillix](https://boards.straightdope.com/u/drachillix)\
**Post date:** [June 20, 2009, 12:43am UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/10 "2009-06-20T00:43:08Z")

</div>

Is there anything like:

pressure boost pumps that may be triggering when not needed?

Air pumps to fill the lines with air (wet dry system) that could be generating excess pressure.

IF its only a single story building that would rule out head pressure from a stuck/malfunctioning check valve.

---

<div class="post-metadata">

**Author:** ![mangeorge](https://avatars.discourse-cdn.com/v4/letter/m/d78d45/32.png) [@mangeorge](https://boards.straightdope.com/u/mangeorge)\
**Post date:** [June 20, 2009, 1:03am UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/11 "2009-06-20T01:03:13Z")

</div>

> [@sailor](#):
>
> Are you serious? How do you think a thermometer works?

The liquid in a common glass thermometer is usually alcohol. And the amount of liquid in the bulb is huge compared to what’s in the tube.

---

<div class="post-metadata">

**Author:** ![Dag\_Otto](https://avatars.discourse-cdn.com/v4/letter/d/439d5e/32.png) [@Dag\_Otto](https://boards.straightdope.com/u/Dag_Otto)\
**Post date:** [June 20, 2009, 1:10am UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/12 "2009-06-20T01:10:30Z")

</div>

I’d guess that it is caused by a jockey pump.

---

<div class="post-metadata">

**Author:** ![mangeorge](https://avatars.discourse-cdn.com/v4/letter/m/d78d45/32.png) [@mangeorge](https://boards.straightdope.com/u/mangeorge)\
**Post date:** [June 20, 2009, 1:13am UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/13 "2009-06-20T01:13:26Z")

</div>

> [@HongKongFooey](#):
>
> We get this problem periodically on some of our systems in the summer months when it gets really hot inside.We had to switch to a different type sprinkler head because the pressure would get high enough to blow one off once in a while.

I’ve never had that happen, but if it does in this application we’re going to have one hell of a mess.  
We’ve had techs from two sprinkler companies, and they all say they’ve never seen any system go up this much. Maybe a few psi, but not 460%.

---

<div class="post-metadata">

**Author:** ![mangeorge](https://avatars.discourse-cdn.com/v4/letter/m/d78d45/32.png) [@mangeorge](https://boards.straightdope.com/u/mangeorge)\
**Post date:** [June 20, 2009, 1:18am UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/14 "2009-06-20T01:18:50Z")

</div>

> [@Dag\_Otto](#):
>
> I’d guess that it is caused by a jockey pump.

There are no pumps in the system.  
It seems to me that if the problem were temperature related, the pressure would return to normal when things cooled down. Unless there’s a check valve.

---

<div class="post-metadata">

**Author:** ![HongKongFooey](https://avatars.discourse-cdn.com/v4/letter/h/c4cdca/32.png) [@HongKongFooey](https://boards.straightdope.com/u/HongKongFooey)\
**Post date:** [June 20, 2009, 1:23am UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/15 "2009-06-20T01:23:13Z")

</div>

> [@mangeorge](#):
>
> I’ve never had that happen, but if it does in this application we’re going to have one hell of a mess.  
> We’ve had techs from two sprinkler companies, and they all say they’ve never seen any system go up this much. Maybe a few psi, but not 460%.

I’ll check tomorrow and see if I can dig up a report to see what they did in our case. It still happens once in a while but it’s not such a big deal if the sprinkler heads can take it. It’s a VERY big deal otherwise.

They did make some changes to keep it from happening as much though. Once in the past two years that I can recall.

---

<div class="post-metadata">

**Author:** ![mangeorge](https://avatars.discourse-cdn.com/v4/letter/m/d78d45/32.png) [@mangeorge](https://boards.straightdope.com/u/mangeorge)\
**Post date:** [June 20, 2009, 1:41am UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/16 "2009-06-20T01:41:33Z")

</div>

> [@HongKongFooey](#):
>
> I’ll check tomorrow and see if I can dig up a report to see what they did in our case. It still happens once in a while but it’s not such a big deal if the sprinkler heads can take it. It’s a VERY big deal otherwise.
> 
> They did make some changes to keep it from happening as much though. Once in the past two years that I can recall.

Wow! I live a sheltered life. I’ve been at this job for 25 years, and have never had a sprinkler head fail. Our weather here is pretty mild.  
We have had a couple function correctly. Grudging kudos from the tennants. 😉  
I’m looking forward to hearing about your problem.

---

<div class="post-metadata">

**Author:** ![sailor](https://avatars.discourse-cdn.com/v4/letter/s/a587f6/32.png) [@sailor](https://boards.straightdope.com/u/sailor)\
**Post date:** [June 20, 2009, 2:00am UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/17 "2009-06-20T02:00:47Z")

</div>

> [@mangeorge](#):
>
> The liquid in a common glass thermometer is usually alcohol.

I am not sure I follow you. Are you saying alcohol expands with heat but water doesn’t? All common materials expand with heat, some more than other.

> [@mangeorge](#):
>
> And the amount of liquid in the bulb is huge compared to what’s in the tube.

What does that have to do with anything? The liquid in a thermometer has empty space into which it can expand. If you have a length of steel pipe full of water the water has nowhere to expand but into the steel and the pressure grows very rapidly.

---

<div class="post-metadata">

**Author:** ![mangeorge](https://avatars.discourse-cdn.com/v4/letter/m/d78d45/32.png) [@mangeorge](https://boards.straightdope.com/u/mangeorge)\
**Post date:** [June 20, 2009, 2:19am UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/18 "2009-06-20T02:19:45Z")

</div>

> [@sailor](#):
>
> I am not sure I follow you. Are you saying alcohol expands with heat but water doesn’t? All common materials expand with heat, some more than other.  
> What does that have to do with anything? The liquid in a thermometer has empty space into which it can expand. If you have a length of steel pipe full of water the water has nowhere to expand but into the steel and the pressure grows very rapidly.

It’s not nice o play dumb in GQ.

---

<div class="post-metadata">

**Author:** ![NinetyWt](https://avatars.discourse-cdn.com/v4/letter/n/cc9497/32.png) [@NinetyWt](https://boards.straightdope.com/u/NinetyWt)\
**Post date:** [June 20, 2009, 2:20am UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/19 "2009-06-20T02:20:08Z")

</div>

**mangeorge** , my previous comment was wrong.

I asked a friend who installs sprinklers and he said high temperatures (as \*\*Hong Kong Fooey \*\*mentions) can cause pressure increases. The company my friend works for often puts pop-off valves in their installations.

---

<div class="post-metadata">

**Author:** ![mangeorge](https://avatars.discourse-cdn.com/v4/letter/m/d78d45/32.png) [@mangeorge](https://boards.straightdope.com/u/mangeorge)\
**Post date:** [June 20, 2009, 2:25am UTC](https://boards.straightdope.com/t/pressure-rise-in-a-fire-sprinkler-system/500332/20 "2009-06-20T02:25:18Z")

</div>

> [@NinetyWt](#):
>
> **mangeorge** , my previous comment was wrong.
> 
> I asked a friend who installs sprinklers and he said high temperatures (as \*\*Hong Kong Fooey \*\*mentions) can cause pressure increases. The company my friend works for often puts pop-off valves in their installations.

That’s what they’re doing with ours. So when the system cools, the pressure should go negative.