> [@HoneyBadgerDC](#):
>
> Each 120v leg has a 30 amp breaker.

Correct. this means that you have only 30 amps of 240 VAC power.

---

<div class="post-metadata">

**Author:** ![HoneyBadgerDC](https://sea3.discourse-cdn.com/straightdope/user_avatar/boards.straightdope.com/honeybadgerdc/32/1033_2.png) [@HoneyBadgerDC](https://boards.straightdope.com/u/HoneyBadgerDC)\
**Post date:** [January 13, 2016, 7:34pm UTC](https://boards.straightdope.com/t/welder-wiring/742767/22 "2016-01-13T19:34:53Z")

</div>

> [@Snnipe\_70E](#):
>
> Correct. this means that you have only 30 amps of 240 VAC power.

I have a 70 amp sub panel, I will check out the wire size going to the outlet, if they will handle 40 amps I might upgrade the breakers to 40 if I have trouble using small rod on the 30 amps. Pretty sure the wire size is 10guage with a 12 foot run to the outlet.

---

<div class="post-metadata">

**Author:** ![Snnipe\_70E](https://avatars.discourse-cdn.com/v4/letter/s/b5a626/32.png) [@Snnipe\_70E](https://boards.straightdope.com/u/Snnipe_70E)\
**Post date:** [January 14, 2016, 12:10am UTC](https://boards.straightdope.com/t/welder-wiring/742767/23 "2016-01-14T00:10:16Z")

</div>

> [@HoneyBadgerDC](#):
>
> I have a 70 amp sub panel, I will check out the wire size going to the outlet, if they will handle 40 amps I might upgrade the breakers to 40 if I have trouble using small rod on the 30 amps. Pretty sure the wire size is 10guage with a 12 foot run to the outlet.

10 gage is good for 30 amps.