Why is my house so difficult to cool? HVAC suggestions needed!

Thanks for the info. I going to replace the whole system anyway with a 19 SEER unit. This one is 10 years old and it has been one nagging problem after another for the last 5-6 years. I figure the electricity savings may not pay for the new one for many years, but reducing the monthly cash flow is something I want to do anyway. I just need to fit the replacement into the schedule and budget. I also want to reinsulate the flex duct into the master bedroom with something that will stay on.

Most of the flex duct made in the past has been R-4. In Ohio, code now requires R-8. The new R-8 flex we’ve bought and installled has been very good stuff. Bigger and a little harder to use (especially in tight spaces) but good stuff. Certainly doable as a DIY project. (and affordable!)

Edit item #6
6a) Temperature of supply air just above evaporator coil
6b) Temperature of supply air at supply register

Your supply duct is under positive pressure so it will not suck in hot air like the return duct will. Still, there shouldn’t be more of a 1-2 degree rise between 6a and 6b. If there is, it is not a sign of broken/leaking ductwork but poor insulation; the Btus from a hot attic are infiltrating the duct and you’re picking up heat in the duct. (As Dag Otto noted. This could be the way to determine if you’re picking up heat in the supply duct)

I’m sure there are a lot of factors; this is probably the biggest.

However, I discovered the other day that I don’t actually have an attic vent.

I went upstairs to perform a cursory examination of the ductwork to see if there were any obvious, gaping holes. There were none visible. I saw from the front of the house the position of the large vent on the brick veneer, just below the peak of the roof. I went back up to the attic to see if any of our attic stuff was blocking a the vent, and realized that there is a sheetrock panel in front of where the vent should be!

There’s obviously space behind the vent in the veneer – that much I can see from the ground level – but how this thing is supposed to work with a slab of sheetrock right behind it has me scratching my head!

1,969 square feet.

I need to get my hands on a thermometer accurate enough to test this. Maybe it’s time for a trip to Fry’s or Home Depot.

I’m not sure. I’d have to go back out there and look at it.

Yes, and yes. We keep it warmer in the day (warmer still when we’re not home), and cool off around bed time when the outside air is already cooler.

Yes, and yes. The ducts in the attic are flexible and wrapped in some kind of silver padding that doubtlessly contains insulation inside. It looks to me like the padding may actually be part of the ducts.

No. The fan only runs when the cooling (or heating - they are both connected together) unit is on.

Both the thermostat and air return are located in the center of the house just beyond the laundry room that functions as an airlock to the garage. There are four air conditioning vents (laundry room, front bathroom, two kids’ rooms) within about a 12 foot radius.

I was up there the other day, but didn’t take notice.

We’ve never had a refrigerant leak. I’m not sure what kind it uses.

Yes, Yes, and only once - just before we moved in.

If I do, I think I will pick a different company other than the one that the home warranty company sent.