  #1  
Old 04-19-2010, 11:04 AM
Zsofia Zsofia is offline
Guest
 
Join Date: Feb 2001
Oh jesus. Fire in the outlet.

Eeek! This morning (after I noticed the boyfriend left the space heater in the bathroom on FOR HOURS while he'd left FOR HOURS with me sleeping in the next room FOR HOURS is he ever in trouble!) I unplugged it and found burn marks on the wider prong of the plug. Examination showed scorching around the plug holes in the outlet as well.

Plugs in that outlet have always been really loose, by the way, and I saw a spark once several months ago. Been meaning to do something about it, but you know how that goes.

It's a GFCI outlet, the only outlet in the bathroom.

So. Obviously that's bad. Is it bad as in "it's just the outlet, replace it and you're fine", or is it bad as in "there's something wrong with the wiring and you should call an electrician"? I've been looking at how to replace it and it seems to be something I could do with a reasonable degree of confidence.
Reply With Quote
Advertisements  
  #2  
Old 04-19-2010, 11:10 AM
johnpost johnpost is offline
Guest
 
Join Date: Jul 2009
Quote:
Originally Posted by Zsofia View Post
So. Obviously that's bad. Is it bad as in "it's just the outlet, replace it and you're fine", or is it bad as in "there's something wrong with the wiring and you should call an electrician"? I've been looking at how to replace it and it seems to be something I could do with a reasonable degree of confidence.
replace the receptacle and you should be OK

plug something into it like a radio turned on and go flip the circuit breaker off or unscrew the fuse. if it stops playing then you can have confidence that the circuit is turned off.
Reply With Quote
  #3  
Old 04-19-2010, 11:17 AM
cornflakes cornflakes is offline
Charter Member
 
Join Date: Aug 1999
Location: Bubbaville
Posts: 4,453
IANAElectrician (and I have always wondered why the mods will allow us to give electrical/plumbing/remodeling advice to strangers when that advice may leave someone dead, and in the meantime threads about minor health issues have been shut down due to the "don't give out medical advice" rule), but...

It sounds like the contacts are loose in the outlet--there isn't any smoke with the heater unplugged. I'd replace the outlet with a commercial grade GFCI (commercial grade outlets tend to have stronger contacts.) While replacing it, I'd check if the insulation on the wires was burned, and I might call an electrician if it was.
Reply With Quote
  #4  
Old 04-19-2010, 11:26 AM
Leaffan Leaffan is offline
Guest
 
Join Date: Aug 2005
Make sure both plugs are not operable before removal; it is possible to wire each half separately, and if you don't know what you're looking for one might be alive whilst the other isn't.
Reply With Quote
  #5  
Old 04-19-2010, 11:31 AM
HongKongFooey HongKongFooey is offline
Guest
 
Join Date: Mar 2008
I'm an electrician and I agree with what johnpost said. You can check the wires in the box for scorching but will probably be able to strip back any damage pretty easily.
Reply With Quote
  #6  
Old 04-19-2010, 11:43 AM
johnpost johnpost is offline
Guest
 
Join Date: Jul 2009
i would second the suggestion of using higher priced receptacles if not commercial grade. though many home improvement stores may only sell one grade of GFCI, you may have to go to an electrical supply store or store where builders buy supplies to find a higher grade.

GFCI units in the box have good instructions and a careful person can do an OK job if they read and understand the instructions. if you have any doubts, uncertainty or fears then get help from a person with experience rather than take a chance at a bad job (which certainly could be a hazard).

for regular receptacles the difference of what is available in a home improvement store is tremendous. the $0.39 receptacles are junk and hazardous and you will replace them every year or risk a fire. you may not want to use a couple dollar commercial receptacle everywhere (though this is a good choice for places you might put plugs in and out of frequently) though you should go for those priced between those points.
Reply With Quote
  #7  
Old 04-19-2010, 12:10 PM
Xema Xema is offline
Guest
 
Join Date: Mar 2002
Quote:
Originally Posted by cornflakes View Post
I have always wondered why the mods will allow us to give electrical/plumbing/remodeling advice to strangers when that advice may leave someone dead, and in the meantime threads about minor health issues have been shut down due to the "don't give out medical advice" rule
[OT]
I wonder this as well. The number of subjects on which the following of random online advice might lead to unpleasant and even dire consequences is essentially unlimited. This seems best handled by a policy of "NB: The value of advice on this message board may be no greater that what you paid for it" - which on the SDMB appears to apply to most but not quite all subjects.
Reply With Quote
  #8  
Old 04-19-2010, 12:36 PM
Zsofia Zsofia is offline
Guest
 
Join Date: Feb 2001
We're always plugging and unplugging with this one - it's the only bathroom receptacle, and between electric toothbrush, heater, hair dryer, and everything else I guess it's no surprise it needs replacing. I'll get the most expensive one they have.
Reply With Quote
  #9  
Old 04-19-2010, 12:41 PM
Zsofia Zsofia is offline
Guest
 
Join Date: Feb 2001
It is funny, by the way - you can say "Yes, sell all your stuff and move to New Zealand to marry that guy you met on the Internet!" and "Oh, hell, yeah, go ahead and rewire that yourself - what's the worst that can happen? Turning off the breaker's for pussies." and "Step one: get a bigger ladder..." but you can't say "Put some aloe on that sunburn and wear sunscreen in the future, dumbass."
Reply With Quote
  #10  
Old 04-19-2010, 01:19 PM
Cheshire Human Cheshire Human is offline
Guest
 
Join Date: Jan 2010
Quote:
Originally Posted by Zsofia View Post
We're always plugging and unplugging with this one - it's the only bathroom receptacle, and between electric toothbrush, heater, hair dryer, and everything else I guess it's no surprise it needs replacing. I'll get the most expensive one they have.
Actually, don't go for the most expensive. Go to a local hardware store, rather than the "big box" home improvement places, and tell them you want the "best quality". Local stores are generally much more knoledgeable about their product lines than "big box" ones. A big box came to our town, but the 2 local ones that survived are still thriving for that very reason. Go in to the "big box" with a problem, and most of their employees can't tell you how to solve it. Go to the local ones and they will bend over backward trying to figure out how you can, and what of their stock you need. If I need a bolt, and know what size I need, the "big box" is closer and more convenient. If I need to solve a problem and don't know how or what I need to do it, I go to the locals and always wind up going home with the best possible solution.

ETA: Also, going that way avoids the problem of relying on us random SDMB yutzes. You WILL be getting advice from pros. They will tell you if the job is beyond you. The "big box" boys won't, because they don't know. It's probably beyond them too.

Last edited by Cheshire Human; 04-19-2010 at 01:23 PM.
Reply With Quote
  #11  
Old 04-19-2010, 01:35 PM
Zsofia Zsofia is offline
Guest
 
Join Date: Feb 2001
Dude, the local hardware stores have vanished. If there are any left, I don't know where they are. They're gone. Hiller went this past year.
Reply With Quote
  #12  
Old 04-19-2010, 02:04 PM
gotpasswords gotpasswords is offline
Charter Member
 
Join Date: Mar 1999
Location: Charlotte
Posts: 13,615
Quote:
Originally Posted by Zsofia
We're always plugging and unplugging with this one - it's the only bathroom receptacle, and between electric toothbrush, heater, hair dryer, and everything else I guess it's no surprise it needs replacing. I'll get the most expensive one they have.
No time like the present to replace the single receptacle with two. If you're insanely lucky, the box inside the wall will be a square box, and just by changing what's called the mud ring for one that holds two devices instead of one, you can do this very easily.

More likely, the entire box will need to be changed. Electrically, this job is very easy for someone who's changed receptacles and switches, but depending on what kind of box is in the wall and how it's attached to the wall, and if that bathroom wall is tiled or not, the job can be tricky from a not wrecking the wall standpoint.
Reply With Quote
  #13  
Old 04-19-2010, 02:09 PM
Gary T Gary T is offline
Member
 
Join Date: Mar 2002
Location: KCMO
Posts: 8,916
Quote:
Originally Posted by cornflakes View Post
IANAElectrician (and I have always wondered why the mods will allow us to give electrical/plumbing/remodeling advice to strangers when that advice may leave someone dead, and in the meantime threads about minor health issues have been shut down due to the "don't give out medical advice" rule...
Quote:
Originally Posted by Xema View Post
[OT]
I wonder this as well. The number of subjects on which the following of random online advice might lead to unpleasant and even dire consequences is essentially unlimited. This seems best handled by a policy of "NB: The value of advice on this message board may be no greater that what you paid for it" - which on the SDMB appears to apply to most but not quite all subjects.
The medical and legal professions are such that the giving of advice, in and of itself, is regulated. A licensed practioner giving unsound advice may incur legal liability, and a layman giving advice at all in these fields may be in violation of law. It's quite a different situation from other fields.
Reply With Quote
  #14  
Old 04-19-2010, 02:16 PM
Zsofia Zsofia is offline
Guest
 
Join Date: Feb 2001
Quote:
Originally Posted by gotpasswords View Post
No time like the present to replace the single receptacle with two. If you're insanely lucky, the box inside the wall will be a square box, and just by changing what's called the mud ring for one that holds two devices instead of one, you can do this very easily.

More likely, the entire box will need to be changed. Electrically, this job is very easy for someone who's changed receptacles and switches, but depending on what kind of box is in the wall and how it's attached to the wall, and if that bathroom wall is tiled or not, the job can be tricky from a not wrecking the wall standpoint.
It's plaster, which I reeeeally don't want to fuck with.
Reply With Quote
  #15  
Old 04-19-2010, 02:45 PM
Philster Philster is offline
Guest
 
Join Date: Aug 2000
If you unplug and plug in items that put a decent load on the outlet/circuit, and your method of turning these items on/off is by plugging and unplugging them then you can shorten the life of the outlet and scorch it.

If at all possible, plug and unplug items when they are 'off'. I know that sometimes it is not possible, but do so when it is.
Reply With Quote
  #16  
Old 04-19-2010, 02:48 PM
Zsofia Zsofia is offline
Guest
 
Join Date: Feb 2001
Oh, we never do that if something has an on switch - I mean, there's not one on, say, an electric toothbrush, but otherwise, yeah.
Reply With Quote
  #17  
Old 04-19-2010, 03:04 PM
Rick Rick is offline
Charter Member
 
Join Date: Aug 1999
Posts: 14,321
Quote:
Originally Posted by johnpost View Post
plug something into it like a radio turned on and go flip the circuit breaker off or unscrew the fuse. if it stops playing then you can have confidence that the circuit is turned off.
I would just like to point out that if your house is wired where the neutral is shared with another circuit, the neutral could still be live even though the receptacle is "dead".
Ask me how I know this.
Reply With Quote
  #18  
Old 04-19-2010, 03:17 PM
t-bonham@scc.net t-bonham@scc.net is offline
Guest
 
Join Date: Mar 2003
Quote:
Originally Posted by Zsofia View Post
Dude, the local hardware stores have vanished. If there are any left, I don't know where they are. They're gone. Hiller went this past year.
They're still out there. You just need to look for them -- they aren't out in big shopping centers like the big box stores.

The Ace coop chain has 4,600 stores in the USA, for example. And True Value also has about 5,000.

Quote:
Originally Posted by Zsofia View Post
It's plaster, which I reeeeally don't want to fuck with.
Plaster is much easier to work with than a tiled bathroom wall -- go for it. I agree with gotpassword that this is a real good time to expand that to a dual receptacle box.
Reply With Quote
  #19  
Old 04-20-2010, 12:24 AM
Terry Kennedy Terry Kennedy is offline
Guest
 
Join Date: Nov 2009
Quote:
Originally Posted by johnpost View Post
plug something into it like a radio turned on and go flip the circuit breaker off or unscrew the fuse. if it stops playing then you can have confidence that the circuit is turned off.
Quote:
Originally Posted by Leaffan View Post
Make sure both plugs are not operable before removal; it is possible to wire each half separately, and if you don't know what you're looking for one might be alive whilst the other isn't.
In addition, I don't think the OP mentioned how old the house is. If the wiring dates back to the 1930's, it may have fuses in both the hot and neutral legs. This can lead to a nasty surprise if you happen to unscrew the neutral. If you have circuit breakers, this won't be a problem.

Even if the wiring is newer than that, the insulating jacket may have become brittle over the years. Older insulation was cloth weave over natural rubber. If you pull the receptacle away from the box and insulation flakes off the wires, stop, leave the power off, and consult a professional.

Otherwise, you should be Ok doing it yourself.
Reply With Quote
  #20  
Old 04-20-2010, 12:44 AM
AClockworkMelon AClockworkMelon is offline
Guest
 
Join Date: Mar 2010
I read the thread title as "Fire in the toilet." I am disappointed. Carry on.
Reply With Quote
  #21  
Old 04-20-2010, 08:51 AM
Zsofia Zsofia is offline
Guest
 
Join Date: Feb 2001
The house is from 1928 but the wiring seems to have been redone in the 90's. (It certainly isn't knob and whatchamacallit!)
Reply With Quote
  #22  
Old 04-20-2010, 08:55 AM
Mr. Duality Mr. Duality is offline
Luminary
 
Join Date: Jul 2001
Location: The High Plains
Posts: 1,167
And get a new boyfriend. This one could well be fatal.
Reply With Quote
  #23  
Old 04-20-2010, 09:08 AM
johnpost johnpost is offline
Guest
 
Join Date: Jul 2009
Quote:
Originally Posted by Zsofia View Post
The house is from 1928 but the wiring seems to have been redone in the 90's. (It certainly isn't knob and whatchamacallit!)
tube

you are in good shape with new wiring.
Reply With Quote
  #24  
Old 04-20-2010, 09:19 AM
aceplace57 aceplace57 is online now
Member
 
Join Date: Oct 2009
Location: CentralArkansas
Posts: 9,974
My electric dryer cord was damaged by loose contacts in an outlet. It had been plugged in for 15 years. The receptacle was at least 30 years old. I guess old age got it.

Funny story. I called an appliance service guy for the dryer. He quickly figured out it was the cord. Replaced the cord and plugged it in. Sparks flew! Very Quickly unplugged it and told me to call an electrician. Wires were badly burned and there wasn't any slack to cut off and reattach. They had to run a new wire.

Last edited by aceplace57; 04-20-2010 at 09:20 AM.
Reply With Quote
  #25  
Old 04-20-2010, 09:47 AM
Chefguy Chefguy is offline
Charter Member
 
Join Date: Jun 2003
Location: Portlandia
Posts: 24,654
You might think about checking the rest of the outlets in your home also. Loose outlets arc, as mentioned. If you've never checked the outlet under your sink which powers the dishwasher and garbage disposal, it's a good idea to do so. Motors usually have a relatively hefty current draw (compared to a lightbulb, for instance), and you want a tight connection for them.

Small embarassing anecdote: when the dishwasher in our old home stopped working, I invoked the Sears warranty and the guy came, tore the thing apart, couldn't find anything wrong, plugged it back in and it worked. A few days later, it quit again. Frustrated, I got down on hands and knees under the sink and pulled out the plug. I'm kneeling there with the plug in my hand and peering around under the sink, when my wife says "how come the plug thingy is all black?" Turns out the problem was a loose outlet, and the plug was burned so badly it wasn't making proper contact. The embarassing part: I was an electrician for 20 years.
Reply With Quote
  #26  
Old 04-20-2010, 10:08 AM
Zsofia Zsofia is offline
Guest
 
Join Date: Feb 2001
Check them as in check for wiggle?
Reply With Quote
  #27  
Old 04-20-2010, 10:42 AM
johnpost johnpost is offline
Guest
 
Join Date: Jul 2009
using a high quality receptacle for locations that you plug and unplug frequently is good because it will last longer between replacement.

it is also good to check receptacles that are left plugged in for long periods for wiggle of the plug and blackness on the prongs. if you see blackness you should clean the prongs to shining metal with sand paper and the receptacle may need replacement. if the plug wiggles then you might bend the prongs slightly in or out and the receptacle may need replacement. either blackness or wiggle are signs of a worn receptacle which is or would become a fire hazard.

in receptacles that remain with a plug in, especially high current draws (freezer, refrigerator, air conditioner, sump pump), it also makes sense to use a quality receptacle. in a quality receptacle the contacts are higher quality and will make and pass the higher current better. it is good to check these receptacles once a year for tightness and if the prongs are not blackened.
Reply With Quote
  #28  
Old 04-20-2010, 11:42 AM
Chefguy Chefguy is offline
Charter Member
 
Join Date: Jun 2003
Location: Portlandia
Posts: 24,654
Quote:
Originally Posted by Zsofia View Post
Check them as in check for wiggle?
Outlets past their prime will be very loose. In some cases, the plug may even fall out by itself. A wiggle test is good, but pull the plug out of the receptacle and check for scorch marks that may indicate arcing, particularly for high-amperage outlets.

Oops, scooped by johnpost.

Last edited by Chefguy; 04-20-2010 at 11:43 AM.
Reply With Quote
  #29  
Old 04-20-2010, 05:16 PM
t-bonham@scc.net t-bonham@scc.net is offline
Guest
 
Join Date: Mar 2003
Quote:
Originally Posted by aceplace57 View Post
My electric dryer cord was damaged by loose contacts in an outlet. It had been plugged in for 15 years. The receptacle was at least 30 years old. I guess old age got it.

Funny story. I called an appliance service guy for the dryer. He quickly figured out it was the cord. Replaced the cord and plugged it in. Sparks flew! Very Quickly unplugged it and told me to call an electrician. Wires were badly burned and there wasn't any slack to cut off and reattach. They had to run a new wire.
The wires wouldn't be badly burned from those sparks if you very quickly unplugged it -- that was scorching/overheating over several years. So replacing the wire was the right thing to do. Given at least 30 years, you got your money's worth out of the old wire.
Reply With Quote
  #30  
Old 04-20-2010, 08:31 PM
UncleFred UncleFred is offline
Guest
 
Join Date: Jan 2008
Quote:
Originally Posted by Philster View Post
If at all possible, plug and unplug items when they are 'off'. I know that sometimes it is not possible, but do so when it is.
We have an 'all-in-one' copier/printer/fax/whatever which has no on/off switch. Plugging/unplugging the line cord is your power on/off.

For some reason this thread reminds me of Kurt Vonnegut's "The Sirens of Titan" (I think it was) where human expatriates on Mars(?) are sent in fleets of flying saucers to invade the Earth. The flying saucers have just 2 controls ; an On switch and an Off switch. The On switch initiates a preprogrammed flight to Earth. The Off switch doesn't do anything, but was put there by Martian mental health experts who knew that humans are only happy with machines they think they can shut off.
Reply With Quote
  #31  
Old 04-22-2010, 05:29 PM
Zsofia Zsofia is offline
Guest
 
Join Date: Feb 2001
Okay, I successfully replaced the outlet. (It wasn't a bigger box, and it was getting dark so I said to hell with it and still only have one.) My question is, why did the instructions specify to do the ground wire with a connecting wire wire-nutted onto the ground that came out of the wall? The old one was like that too, which confused the hell out of me. What's the advantage there?
Reply With Quote
  #32  
Old 04-22-2010, 05:43 PM
Peremensoe Peremensoe is offline
Guest
 
Join Date: Apr 2010
Quote:
Originally Posted by Zsofia View Post
My question is, why did the instructions specify to do the ground wire with a connecting wire wire-nutted onto the ground that came out of the wall? The old one was like that too, which confused the hell out of me. What's the advantage there?
You mean that the receptacle had a green terminal screw, with a segment of wire attached, which in turn was nutted to a wire in the box--part of the house wiring?

There's no advantage to that, unless the house wire is so short that it's hard to get it on the terminal screw.

A few devices don't have the terminal screw, but simply a green wire.
Reply With Quote
  #33  
Old 04-22-2010, 05:46 PM
boytyperanma boytyperanma is offline
Guest
 
Join Date: Dec 2005
Quote:
Originally Posted by Zsofia View Post
Okay, I successfully replaced the outlet. (It wasn't a bigger box, and it was getting dark so I said to hell with it and still only have one.) My question is, why did the instructions specify to do the ground wire with a connecting wire wire-nutted onto the ground that came out of the wall? The old one was like that too, which confused the hell out of me. What's the advantage there?
There is an assumption with outlets you will be doing them in series. There are 2 lugs for the neutral and the hot but only one for the ground. So in order to put use an outlet in series you would have to wire nut the ground. ie they say that so idiots don't try and put two wires under the one ground lug.
Reply With Quote
  #34  
Old 04-22-2010, 05:46 PM
Zsofia Zsofia is offline
Guest
 
Join Date: Feb 2001
The instructions told me to use a piece of wire specifically and connect it - I had the one that had been attached to the previous box.

ETA - these were the instructions for an outlet not in a series - they were separate instructions.

Last edited by Zsofia; 04-22-2010 at 05:47 PM.
Reply With Quote
  #35  
Old 04-22-2010, 05:49 PM
johnpost johnpost is offline
Guest
 
Join Date: Jul 2009
Quote:
Originally Posted by Zsofia View Post
Okay, I successfully replaced the outlet. My question is, why did the instructions specify to do the ground wire with a connecting wire wire-nutted onto the ground that came out of the wall? The old one was like that too, which confused the hell out of me. What's the advantage there?
Good doing.

you would use a wire nut (USA brand/term of wire connector) because of multiple wires. You might have the GFCI feeding other receptacles needing another wire, it also common to have a wire fasten to the box itself (if metal), other situations could add another ground wire.
Reply With Quote
  #36  
Old 04-22-2010, 05:52 PM
Peremensoe Peremensoe is offline
Guest
 
Join Date: Apr 2010
Quote:
Originally Posted by boytyperanma View Post
There is an assumption with outlets you will be doing them in series. There are 2 lugs for the neutral and the hot but only one for the ground. So in order to put use an outlet in series you would have to wire nut the ground. ie they say that so idiots don't try and put two wires under the one ground lug.
Unless it's half-switched, I always pigtail hot in/hot out and neutral in/neutral out together anyway--that's safer than using the terminal screws. And for the ground, that kind of pigtailing is required by code no matter what the device or circuit configuration.

But wait, this is a GFI we're talking about? Zsofia, are you sure your wires are on the "line" side terminals?

Last edited by Peremensoe; 04-22-2010 at 05:54 PM.
Reply With Quote
  #37  
Old 04-22-2010, 06:30 PM
Zsofia Zsofia is offline
Guest
 
Join Date: Feb 2001
There's only one outlet in the bathroom. It's fault protecting itself. Just one cord coming into the box. Nothing coming out. Three wires.
Reply With Quote
  #38  
Old 04-22-2010, 07:02 PM
johnpost johnpost is offline
Guest
 
Join Date: Jul 2009
Quote:
Originally Posted by Zsofia View Post
There's only one outlet in the bathroom. It's fault protecting itself. Just one cord coming into the box. Nothing coming out. Three wires.
you would have the grounding wire on the incoming cable, a wire to the grounding screw on the box (if metal), a wire to the GFCI, three wires connected with a wire nut.

if you had a plastic box then the grounding wire on the incoming cable could go right to the GFCI.
Reply With Quote
  #39  
Old 04-22-2010, 08:49 PM
Kevbo Kevbo is offline
Guest
 
Join Date: May 2005
Am I the only one that expected this thread to be about Mexican food?
Reply With Quote
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 02:34 AM.


Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2013, Jelsoft Enterprises Ltd.

Send questions for Cecil Adams to: cecil@chicagoreader.com

Send comments about this website to: webmaster@straightdope.com

Terms of Use / Privacy Policy

Advertise on the Straight Dope!
(Your direct line to thousands of the smartest, hippest people on the planet, plus a few total dipsticks.)

Publishers - interested in subscribing to the Straight Dope?
Write to: sdsubscriptions@chicagoreader.com.

Copyright © 2013 Sun-Times Media, LLC.