Residential sprinklers - a subject near and dear to my heart.
Firstly, there are three different sections of the National Fire Codes that we are dealing with. The first is NFPA 13, Standard for the Installation of Sprinkler Systems. That covers most systems. There are two other sections, though, that cover what we’re talking about. NFPA 13D, Standard for the Installation of Sprinkler Systems in One- and Two-Family Dwellings and Manufactured Homes, and NFPA 13R, Standard for the Installation of Sprinkler Systems in Residential Occupancies up to and Including Four Stories in Height. The 13D systems are what we’re dealing with in this case.
NFPA 13D was first published in 1975, after a two-year writing and vetting process. Residential sprinklers have been available since the late 1960s. NFPA 13 (for the big systems) has been around since 1896.
Residential sprinkler systems are not exactly like those found in commerical and other large buildings. Think of them as a much smaller cousin. They do not have to meet nearly as many requirements as a commerical system, thus they are a boatload less expensive.
- A regular NFPA 13 system needs a minimum of a 6" water main and a long duration water supply (upwards of 3 hours, depending on the size of the system). A 13D needs no water main (so you can use a well) and a 10 minute water supply.
- The water flow in a NFPA 13 system is calculated based on the expected hazard in the building, how much water per square foot is needed for that hazard, and how many square feet that that quantity of water is needed on. You can expect capacities greater than 1500 gpm for an NFPA 13 system. For a 13D, you generally only need to provide the flow capacity for two sprinkler heads.
- Speaking of sprinkler heads, a normal NFPA 13 system needs a minimum of 1/2" heads, flowing about 35 gpm at 50psi. They can go as big as 1-1/2" heads flowing upwards of 250 gpm in some applications like high rack storage warehousing. A residential sprinkler head is designed to activate sooner (called a quick-response head), if it goes off sooner, the fire is smaller, and less water is needed. A residential head can have flows as low as 18 gpm.
- Plastic pipe can be used in a 13D system (CPVC), you do not need black iron threaded or steel grooved piping like an NFPA 13 system.
- No fire department connection (a hose connection for firefighters to add water to a sprinkler system) is required on a 13D system (although it’s a good idea to have one). It is requried on a NFPA 13 system
- No special valving system is required on a 13D system (no alarm check valve, usually no backflow prevention, only one indicating valve, etc)
- No outside alarm system is required (either a mechanical or electrical alarm outside to indicate the system is operating)
That’s off the top of my head. The list goes on, I don’t have the time to do a complete side-by-side comparison of the codes.
As was said above, they run about $1/square foot to install. Installation in new buildings, obviously, is much cheaper than in existing buildings. Here in Massachusetts, I’ve heard that starting in 2012 they’ll be required in all new construction. About time, if you ask me.
There are a couple of streets in my town where the developer chose to install residential sprinklers, and there are a number of individual houses elsewhere with them. I have not had to respond to a house fire in any of the sprinklered homes, but the fires I have gone to in unsprinklered homes would have been much smaller had sprinklers been present.
A fire in today’s homes can remove your exit choices in less than a minute from igniton, and can produce sufficient combustion byproducts to incapacitate anyone inside in two to three minutes. Smoke detection is (usually) great, but it doesn’t put water on the fire. Residential sprinklers buy you the time to get out of the house safely. When all is said and done, the fire may be smaller than it would have been, but that’s not the goal of a 13D system - it’s purely for additional evacuation time.
There are a few good videos on YouTube of residential sprinklers operating. I do like the PSA from Fresno, CA on the topic, too.