US systems tend to have only one protective device, whereas UK systems will have two, and if you counts the incomer fuse then its three.
The UK plug may be large, but it contains a silica sand fuse, and this prevents tracking across the carrier, which matters in events such as crowbar short circuits.
Our systems is that of one ring main with any number of outlets connected, the protective device backing that up will be between 30A(not common) to 60A(rare).This circuit board fuse has only one purpose, to protect the house wiring - it is not there to protect the appliance at all. If there is a RCD installed then it will protect users from earth faults
The problem here is that the flex is rated only for a maximum of 15 amps, and that would only be on heavier current appliances and extension leads. The majority of appliance flex will be rated at less than 15A, more likely around 7A or under - which means that the protective device could readily carry a current of , say 20-30A without operating, and the 7A flex is just going to melt and start a fire.
This is why we need a fuse in the plug, that fuse will be rate for the flex, and not - as most people believe - to the appliance.
Our plugs may seem large, however I have seen enough of them burned out - especially n the bad old days when people used socket adaptors such as these
If folk did not have enough outlets they would add in an adaptor, and then add another adaptor into the adaptor. The weight of all these plugs and adaptors on an outlet would reduce the friction contact, it was too much for the strength of the outlet contact springs - result is you get heating of the contacts due to higher resistance. It takes a while but this will generally degrade the plastics in the plug and outlet - and this leads to a vicious cycle where heat degradation increases contact resistance further and so increases the amount of heat produced further.
I don’t know the specific ratings of the US 110V system and the outlets but they do not appear to me to be capable of handling 13A, they only look to be good for maybe 5A - and that surely means that you can only use appliances up to around 500Watts - whereas our outlets will go up to 2.5KW