The cause of the blackout isn’t clear at this stage. However, there are three possible scenarios:
1) Thermal overload.
This is the easiest to explain, but probably not what happened.
All of the transmission lines have limits on the current that they can carry. The current is constantly monitored, and if the limit is exceeded, say because of a fault (short circuit) on the line, circuit breakers at both ends of the line will open. The current that the line was carrying will be redistributed amongst the remaining lines.
The system is supposed to be operated in such a way that it can survive the loss of any transmission element. If it isn’t, the loss of one line can cause the overloading of another, which will then also trip, and so on.
2) Transient instability.
This is a bit more complicated. When there is a fault on a transmission line, the load on some generators is increased, whilst the load on others is reduced.
Normally, all of the generators spin at exactly the same speed, 3,600 rpm.
During the fault, generators with increased loads will begin to slow down a bit. The others will begin to speed up a bit. When the fault is removed by the circuit breakers on the transmisison line, the generators all have to return to the same speed. The slow ones speed up by drawing power from the faster ones, via the transmision lines that are still in service.
Again, the system is supposed to be operated in such a way that it can survive the re-synchronising of the generators.
3) Steady-state instability.
All of the generators and some transmission lines have control systems that monitor voltages, currents, and speeds. The control systems will respond in various ways. For example, a generator’s governor will respond to a slowing of the generator by increasing the boiler output or turbine fuel feed.
In some situations, a response from one control system can provoke an opposing response from another control system somewhere else. The first control system responds more strongly, which provokes an even bigger response from the second one, and so on. This can cause increasingly large oscillations in the current flows on transmission lines, until they begin to trip off.
And yet again, the system is supposed to be designed and operated in such a way that behaviour doesn’t occur.