Hey EEs, Electricians etc, have a weird one for you

So today I had to set up for a gig at the Giant Convention Center, audio and lighting for about 5000 people. Daisy chained 2 Portable Power Distros, Via pass throughs, tied into their service with Cam Locs, 200 amp 3 phase. The cams they gave me were tied into an isolation transformer(dirty power). Volt meter says +/- 120v per leg, cyclic rate was a tad low about 59.2hz avg.

So the question

A leg to B leg 208v, B leg to C leg 208v, A leg to C leg 208v, used two different meters same result, what gives?

I am used to seeing 208v between, say, A and C but then you usually get 220v between the other two.

I have more info if you need it and truthfully it does not matter as none of the gear needs 220v but I have been scratching my head over this for a couple of hours and I cannot for the life of me come up with a reason for this other than the transformers wiring and why in the heck would you wire a transformer that way? This is all under no load BTW.

Thoughts anyone?

Thank You

Capt

Three phase voltage in the US is typically 208 phase to phase and 120 phase to ground.

Doh, I was having a brain fart you are correct Sir 120 x 1.732= 207.84. Sorry not enough sleep.

Capt

**Chefguy **has it.

What’s going on is that each leg is 120 degrees out of phase from the next, and you get a different result from subtracting any two legs than you get if you subtract zero (i.e., ground) from one leg.

Or, in trig identity form:
sin(x) - sin(x+120) = sqrt(3)*sin(x - 30)

That sqrt(3) provides the difference in amplitude. If one leg by itself is 120, then the difference between any two has amplitude 120*1.732 = 207.846.

This is why Rock and Roll should not start at the crack of dawn, it makes my brain hurt. Thanks for reminding me what I already knew. Doh:smack:

Capt

All that noise has caused dain bramage.

Ah That is It! Won’t my Mother be proud. :smiley:

Capt