I think I have an understanding of what’s going on, but I want to be sure I’m not missing anything.
My sister has an older house (~1950s) and wants to install an EV charger. I’m giving them a spare mobile charger, so they just need a 14-50 receptacle to be installed.
They took a look at their setup and found a few unusual things. First: there’s no main breaker. They sent me some photos of the main panel, though, and I believe it’s what’s called a split-bus panel.
These are older and obsolete, but basically: the electrical code allows up to 6 breakers (or “service disconnecting means”) to be connected directly to the service conductors. So, the top part of the panel has 6 slots for breakers, which have no upstream main breaker.
One of these slots has a 60 A breaker which is connected to the bottom half the panel, which has the normal collection of 15-amp breakers for lighting, etc. (hence the “split” between top and bottom half)
There are two other breakers in the top half: a 30 A going to the air conditioner, and a 100 A going to a subpanel (which has some heavy loads, like an electric range and washer/dryer). The box has a rating of 150 A.
So already there’s something I find weird: we have 100+60+30=190 A of breakers on a 150 A panel, with no upstream main breaker. However, NEC 230.90 Exception 3 says:
The sum of the ratings of two to six circuit service disconnecting means can exceed the ampacity of the service conductors, provided the calculated load in accordance with Article 220 does not exceed the ampacity of the service conductors.
So it seems ok, assuming the load calculation was done. Which leaves the question of the EV charger.
I think, based on this, that they can install a 50 A breaker in the upper part of the panel (there are 3 free slots) and wire it to a receptacle (which doesn’t need to be far away). And this will be to code as long as they perform a whole-house load calculation and it falls under the limit. Which would take into account the fact that the EV charger is only drawing 32 amps max, for instance, that not all appliances are going at once, etc.
Anything I’m missing here? Anyone else have to deal with these split-bus panels?