UK electrical regulations may be very differant to the US, especially because all our domestic supplies run on 220V, and every single appliance has a fuse built into the plug, which I belive is differant to the US where in the case of 110V circuits you just use 2 pin unfused plug.
That disclaimer being made, what you first need to consider, is what we in the UK call electrical diversity, that is, the number of appliances that will be energised at any time, which is not the same as the worst case scenario of everything being switched on.
Think about which circuits lead to which outlets, and then add up the wattage of all appliances likely to be running from it.
Next, you need to look at the number of outlets you wish to add, and sum in the wattage that these will be supplying.
Add both these figures together, and divide this total, by you supply voltage, ie 110V, and this will give you the current that you are wishing to draw from the circuit.
Your next issue is to consider the cross section area of your circuit cables, now you in the US use a.w.g whereas we in Europe use mm[sup]2[/sup] square millitmetres.
Since I don’t have the chart available, you will need to look this up, there will definately be something on the net.
Your circuit wiring obviously needs to be able to carry this current continuously so if they are running at or near the limit for the size of your supply cables, then it a case of running a comlpetely fresh circuit from your distribution board.
Personally, I would not be wanting to run a large heater such as you describe on the same circuit as IT and electronic equipment from the same circuit, in fact, looking at your current total applainces, I would say that you really should consider running another circuit completely.
It is much more than a matter of looking at your normal operating current, you would also need to consider what happens when fault conditions occur, the nominal gauge of supply wires from current delivery consderations is usually enough, but not always, sometimes you may have to use a wire size larger than you would expect due to special requirments such as long cable runs - above 50-100 yards, or going through very warm environments such as near a house furnace.
I have left out considerations about the fuse disconnection times and circuit impedance as your electrical system is such that a US poster would be better advised, but in my experience, you can get away with a whole lot more if you use GFCI devices as they tolerate a much lower level of fault current than do fuses and so they disconnect much faster.