[QUOTE=Q.E.D.]
One of the main things that causes evaporator line freezing is low gas pressure. If you’ve cleaned or changed the filters and vacuumed the dust, dirt and debris out of the evap coils (this will be the part indoors with a filter and a fan to blow air over it and through the ductwork) then low gas pressure is a good bet, particularly if the system ran fine last year.
[/QUOTE]
[Emphasis mine]
I hear this a lot, but IME (26 years and counting) the main cause of evap freezeup is low air flow across the evaporator coil. As noted, this can be caused by dirty filters (already checked), dirty evaporator coil (the usual culprit), excessively dirty or failing evaporator fan (rare), restricted supply air ductwork or restricted return air ductwork (rarer still).
However, low refrigerant levels will also cause freezeups. Doubly so because once ice builds on the evaporator coil, airflow basically stops, which kind of snowballs the process.
I have also seen low evaporator air flow diagnosed as low refrigerant charge by inexperienced technicians, since one of the effects of restricted airflow is a reduced suction pressure.
A rough way to test if the problem is low refrigerant charge is to run just the indoor fan without the compressor for a few hours to ensure that all of the ice on the evaporator coil has melted. You can do this by switching the “heat-off-cool” switch to Off and the Fan switch to On on your thermostat. Once you are sure all of the ice has melted, move the thermostat switch back to the “cool” position and immediately check the refrigerant suction line at the outside unit (the condenser). If the suction line at the condenser does not get cold enough to sweat, like a glass of iced tea, within a few minutes, you probably have a low refrigerant charge. OTOH, if the line immediately gets very cold, possibly even forming frost, you likely have a clogged evaporator coil.
For a low refrigerant condition, the repair is to carefully check for leaks (the access ports where the refrigerant gauges are connected is a routine source of small leaks - lines rubbing against nails in the walls or attic is another) and then top off the charge.
For a restricted evaporator coil problem, the remedy is to remove the source of restriction. This is almost always a dirty evaporator coil and involves gaining access to the inlet side of the coil and brushing out the surface debris and then soaking with a self-rinsing coil cleaner. Oftentimes, this operation is followed shortly by a clogged drain line as the debris tries to flow through the line.